My boiler is over pressurising, and venting out of the PRV outside (Continually dropping) I have replaced the PRV and checked the expansion vessel that needed topping up. I did notice that when I had toped up the Expansion vessel that the water gauge when up to the pressure that I had put into the expansion vessel? is that right ???
THe pressure goes right up to 4 bar when the heating is on and then drops back to 2.5 Bar when heating is off.
I suspect the expansion vessel? is there any way this can be checked/ tested except recharging it to the correct pressure ??
THe pressure goes right up to 4 bar when the heating is on and then drops back to 2.5 Bar when heating is off.
I suspect the expansion vessel? is there any way this can be checked/ tested except recharging it to the correct pressure ??