Had to look at this today.
Fault code 10 (flame not detected).
Boiler was actually firing up, but not rectifying. Checked the leads all had continuity through them. Took the flame electrode out and it looked pretty bad. Cleaned it up, popped it back and it them fired up. I've ordered a new one, but is there any common problems on these that could cause this?
19.5 mbar on ignition, gas valve breather tube clear.
Also, I couldn't get it to go in to max service mode, despite following the M.I.s. Any ideas?