I was wondering if anyone may have experienced similar problems to me with this combi boiler (Vokera Unica He).

The boiler has been installed 3 years and has had light use. The boiler is installed in a bedroom and has a flue to an external wall.

Over the past 4-5 weeks I noticed the boiler was becoming more noisy when switched off. The fan sounds like it is running constantly. After a few weeks of this, one day the boiler failed to ignite with the error code stating there was a problem with the Tacho/Fan.

I reset the boiler, set to heating and it started working normally again for about a week then same error code. If I left the boiler set to heating with the thermostat controlling the demand for heating 24/7 (I would set thermostat to low to switch off and turn up when I wanted heat) it seemed to work fine for a couple of weeks until it failed again with the same error code. The error then became more and more frequent to the point where I couldn't get it to fire at all.

It has been off for a week now but I managed to get it to fire today by first getting it to fire and heat hot water then switch it to central heating. Since the error I've never got the boiler to fire when switched to CH I've always had to get the water heating first. It was intermittentently working at first today but is now fully operational I am hoping this means there may not be too much wrong with it.

Any thoughts would be greatly appreciated!
 
I was wondering if anyone may have experienced similar problems to me with this combi boiler (Vokera Unica He).

The boiler has been installed 3 years and has had light use. The boiler is installed in a bedroom and has a flue to an external wall.

Over the past 4-5 weeks I noticed the boiler was becoming more noisy when switched off. The fan sounds like it is running constantly. After a few weeks of this, one day the boiler failed to ignite with the error code stating there was a problem with the Tacho/Fan.

I reset the boiler, set to heating and it started working normally again for about a week then same error code. If I left the boiler set to heating with the thermostat controlling the demand for heating 24/7 (I would set thermostat to low to switch off and turn up when I wanted heat) it seemed to work fine for a couple of weeks until it failed again with the same error code. The error then became more and more frequent to the point where I couldn't get it to fire at all.

It has been off for a week now but I managed to get it to fire today by first getting it to fire and heat hot water then switch it to central heating. Since the error I've never got the boiler to fire when switched to CH I've always had to get the water heating first. It was intermittentently working at first today but is now fully operational I am hoping this means there may not be too much wrong with it.

Any thoughts would be greatly appreciated!

I think it's gona be time to call a local engineer in

What's your location?
 
Vokera when they first brought these out had a problem with the air vent in the top right corner leaking. The leak ran down the connected tube and dripped on to the fan causing problems, usually blown fan ( thick end of £300 to buy, They now have designed a shield which covers the fan should it happen). It might be worth checking to see if this has happened first.
 
Vokera when they first brought these out had a problem with the air vent in the top right corner leaking. The leak ran down the connected tube and dripped on to the fan causing problems, usually blown fan ( thick end of £300 to buy, They now have designed a shield which covers the fan should it happen). It might be worth checking to see if this has happened first.

Wouldn't that come with a replacement fan?
 
Not a 100% sure as i had a couple of occurences which failed under warranty, so had Vokera out and noticed the cover installed and it is now standard on all new boilers. This was happening approx 2-3 years since which would fit the posts timeframe.
 
I think it's gona be time to call a local engineer in

What's your location?

Hi Simon, cheers, I have the number of a recommended local engineer...I just haven't dared ring him yet! I thought this problem may be unique to this boiler and it wouldn't do any harm to gather some information via peoples experiences on here.
 
Not a 100% sure as i had a couple of occurences which failed under warranty, so had Vokera out and noticed the cover installed and it is now standard on all new boilers. This was happening approx 2-3 years since which would fit the posts timeframe.

Thanks Woodsy. I have read a little bit about this online. Maybe my fan has lasted past the warranty due to light use?
If the boiler has failed due to a "design fault" do you think I may qualify for a reduced cost fan replacement (if this is the fault) as my boiler is out of warranty?

I was hoping the boiler wasn't going to need the fan replacing after only 3 years as it's a rather expensive part!
 
I found it happened when the boiler was topped up. Ask your engineer to a) see whether it is the origonal model, ie no shield and b) if it looks like it has happened and then speak to Vokera and ask the question. good luck.
 
Not particulary but price for the fan is a joke. At the time i seem to remember it was £290 plus vat. Didn't bother ringing round as the second time it happened to me the boiler was 2months out of its 2yrs warranty, so i rang the rep and he sorted it for me. tbh the price of spares generally are ridiculous. I think that the fan and pcb alone come to the price of a new boiler.
 
Last edited:
spares that pricey would make me not fit that brand,thats one of the reasons i fit baxi spares are reasonable fan on a duotec is 78+vat
 
Went on the Baxi course last week for the new Neta tec and duotec for that reason. Generally Unica is a good boiler if a bit old fashioned in its internal layout. Problem now is selling the extra cost of the duotec on to the customers who generally don't want to pay even the cost of the Unica.
 
Went on the Baxi course last week for the new Neta tec and duotec for that reason. Generally Unica is a good boiler if a bit old fashioned in its internal layout. Problem now is selling the extra cost of the duotec on to the customers who generally don't want to pay even the cost of the Unica.
id show them the diffence in the parts prices
 
I usually like vokeras but the unica is a banger in my experience. They've really let themselves down with the unica
 
That's not really what I want to hear! ;)

Sorry mate, I think most who do repairs would agree.
I went to a 'mynute he' which is pretty much the same boiler internally except it's a heat only boiler. The rubber hose (cheapskate option, i dont understand whats wrong making a pipe in copper these days) had leaked onto the transformer. So the pipe needed replacing along with the transformer. Parts alone came to £120 inc vat, this system had 18 rads above the boiler so the labour costs where very high.

I'm not impressed with them at all
 
I've just had a chat with an engineer who is coming to have a look at my boiler at the weekend.

Without looking at the boiler his advice was that it may be best to invest money in a more reliable boiler rather than waste money repairing the Vokera.

As the fan is running constantly he suggested it could be a fault with the PCB?

Would water leaking on the fan cause a short of somekind leading to the fan running constantly?
 
I've just had a chat with an engineer who is coming to have a look at my boiler at the weekend.

Without looking at the boiler his advice was that it may be best to invest money in a more reliable boiler rather than waste money repairing the Vokera.

As the fan is running constantly he suggested it could be a fault with the PCB?

Would water leaking on the fan cause a short of somekind leading to the fan running constantly?

I would call a different engineer

This one sounds like he hasn't done many breakdowns on modulating fans
 
I would call a different engineer

This one sounds like he hasn't done many breakdowns on modulating fans

Hi Simon, thanks for taking an interest again. My heating was on all night enough to warm the place up and then failed again this afternoon. I've not managed to resart it but I should be safe from hypothermia tonight! It's possible I haven't described the unit properly to the engineer. I didn't mention the model just the make. The engineer was recommended by my Dad and his friend so if it all goes wrong I can blame them ha ha!

As you've mentioned modulating...the fan does still modulate and where I initially thought it was noisy it is in fact just running constantly even when there is no demand for hot water or CH.

When I first power the unit up the fan accelerates up quickly then settles down to what I would consider to be a quite a high RPM and sits at that RPM constantly. When a tap is turned on the fan raises in RPM and when the error clicks in the fan revs up then settles down again similar to initial power up. This all seem fairly normal to me (obviously no expert) appart from the constant running.

I don't know how these things work but I assume there is a sensor or switch that is telling the fan it needs to run?

Do you have any thoughts on diagnosis Simon?
 
Hi Simon, thanks for taking an interest again. My heating was on all night enough to warm the place up and then failed again this afternoon. I've not managed to resart it but I should be safe from hypothermia tonight! It's possible I haven't described the unit properly to the engineer. I didn't mention the model just the make. The engineer was recommended by my Dad and his friend so if it all goes wrong I can blame them ha ha!

As you've mentioned modulating...the fan does still modulate and where I initially thought it was noisy it is in fact just running constantly even when there is no demand for hot water or CH.

When I first power the unit up the fan accelerates up quickly then settles down to what I would consider to be a quite a high RPM and sits at that RPM constantly. When a tap is turned on the fan raises in RPM and when the error clicks in the fan revs up then settles down again similar to initial power up. This all seem fairly normal to me (obviously no expert) appart from the constant running.

I don't know how these things work but I assume there is a sensor or switch that is telling the fan it needs to run?

Do you have any thoughts on diagnosis Simon?

Don't really like to say to much. But I would steer away from a pcb
 
First, i would disagree with your engineers opinion- boiler is a decent boiler for its price range, if a little dear on the spare parts, i've fitted approx 70 with only the two faults i described earlier and service approx half of those fitted. As your not gsr i don't want to speculate much more than already done but a decent engineer or vokeras fixed price repair should sort it and at 3yr old would be worth it.
 
Engineer came out on Saturday just to have a look as his tools were left in a customers house (something like that). He thought I may have had a flow chart showing the ignition proceedure but there is nothing in the Vokera documentation. He said that my boiler should ignite when first powered up and that this wasn't happening.

After a while he admitted he had no experience of these boilers and mainly just dealt with installation of Baxi boilers and didn't really do fault finding. He said he would pass my number and the details of the fault on to his mate who was an expert at fault finding. I was told on Saturday morning I would receive a call in the next 4-6 hours...it is now late Monday night and I have yet to hear anything. I have been too busy today to do anything about it.
 
Engineer came out on Saturday just to have a look as his tools were left in a customers house (something like that). He thought I may have had a flow chart showing the ignition proceedure but there is nothing in the Vokera documentation. He said that my boiler should ignite when first powered up and that this wasn't happening.

After a while he admitted he had no experience of these boilers and mainly just dealt with installation of Baxi boilers and didn't really do fault finding. He said he would pass my number and the details of the fault on to his mate who was an expert at fault finding. I was told on Saturday morning I would receive a call in the next 4-6 hours...it is now late Monday night and I have yet to hear anything. I have been too busy today to do anything about it.

why dont you have one of us come around and help
 
Status
Not open for further replies.

Similar plumbing topics

This response doesn't make any sense, as the...
Replies
23
Views
2K
S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
180
S
The housing association I work for only get...
Replies
4
Views
1K
new p.h. ex. that will be alot cheaper than a...
Replies
5
Views
955
Nothing you can check yourself as it states in...
Replies
1
Views
1K
Deleted member 120897
D
Back
Top