Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss vokera vision C30 in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
D

derrybongo

hi all

just had a quote from a gas safe installer who says its ok to install this boiler with 15mm gas supply as there is no other gas appliances in the property,

anybody know anything about this boiler
 
how longs the run?

but cant see esp with a 30kw boiler
 
If the connection at the boiler is 22 then manufacturers advice no less , check manufacturer specs. Most 30kws are 22mm , km at even need 28 depending on length of run.
 
Best to upgrade the 3m run to 22mm to be right.
 
the manafacturers book says no less than the boiler inlet which is 15mm. I think there is approx 8 metres of 22 mm to the kitchen from the meter and then 3m of 15mm to the boiler
 
the manafacturers book says no less than the boiler inlet which is 15mm. I think there is approx 8 metres of 22 mm to the kitchen from the meter and then 3m of 15mm to the boiler

defo need 22mm depending on elbows/route may need a length of 28
 
cant understand why the manafacturers installation manual would not insist on this
 
cant understand why the manafacturers installation manual would not insist on this

its down to the installer to work the gas.cold water and hot water needs out
 
i presume the guy who has fitted the boiler has done this and said its ok and has signed off the benchmaark sheet
 
i presume the guy who has fitted the boiler has done this and said its ok and has signed off the benchmaark sheet

its down to him/the installer, and whos going to get it in the neck when it goes wrong
 
3m of straight 15mm pipe will give a drop of 1mb (max drop allowed) on its own to a 30kw boiler never mind the rest of the pipe or any bends.
It needs upgrading period :)
 
3m of straight 15mm pipe will give a drop of 1mb (max drop allowed) on its own to a 30kw boiler never mind the rest of the pipe or any bends.
It needs upgrading period :)

1.5mb now :) well on Worcesters it is
 
Unfortunately some installers leave a lot to be desired due to being to thick or too lazy or just couldn't care less.
 
Status
Not open for further replies.

Similar plumbing topics

Ok I think I see what your saying mate, So...
Replies
9
Views
731
M
We would need more information but I would...
Replies
1
Views
746
Deleted member 120897
D
Hi Chris, Are there any specialists in east...
Replies
4
Views
757
T
  • Question
Sounds OK so long as the heating system is...
Replies
2
Views
310
If he's cautious, the plumber will want to...
Replies
3
Views
676
Back
Top