Shetlandplumber
Hi all, first time poster here so hope you can help!
Got called to a boiler breakdown today with the customer complaining of lukewarm hot water. Had a look at the boiler and it is a warmflow 70-90 combi (with the flexible braided pipes inside)
I've seen before with them the flexible pipes being clogged with debris so I drained the boiler and checked but they are both clear. I thought it must then be the thermostatic mixer in the boiler so I replaced it with no success. I presumed the hot water circulating pump must not be moving enough water so I replaced it but that did not help either! The hot water is still running warm (48 oC) for a moment the lukewarm (38oC) after that.
The primary flow side of the plate heat exchanger is very hot, return side slightly colder and pipe from the heat exchanger to the mixing valve lukewarm. I called warmflow technical help and the suggested it must be the plate heat exchanger at fault but I though I would see if anyone here knew of anything else before ordering a new one. Some other threads have mentioned check valves in the pump housing? Any help is greatly appreciated!
Thanks!
Got called to a boiler breakdown today with the customer complaining of lukewarm hot water. Had a look at the boiler and it is a warmflow 70-90 combi (with the flexible braided pipes inside)
I've seen before with them the flexible pipes being clogged with debris so I drained the boiler and checked but they are both clear. I thought it must then be the thermostatic mixer in the boiler so I replaced it with no success. I presumed the hot water circulating pump must not be moving enough water so I replaced it but that did not help either! The hot water is still running warm (48 oC) for a moment the lukewarm (38oC) after that.
The primary flow side of the plate heat exchanger is very hot, return side slightly colder and pipe from the heat exchanger to the mixing valve lukewarm. I called warmflow technical help and the suggested it must be the plate heat exchanger at fault but I though I would see if anyone here knew of anything else before ordering a new one. Some other threads have mentioned check valves in the pump housing? Any help is greatly appreciated!
Thanks!