I have gradually fitted smart TRV's to all of the radiators in our house, and in general we are very pleased with them. However, it has become apparent that quite often, when the timing makes the TRV switch off, this sets off water hammer in that radiator. This is easily fixed by running a hot water tap anywhere, but it is a nuisance. It would appear that the pump doesn't like the sudden switch off - understandable but I am surprised that I can find no mention of this problem anywhere. It surely is quite (very?) common. And is there anything that can be done about it? Now we think we understand the issue we have arranged a sort of partial workround for the end of the day - ie the CH to close down in the evening at 9.45pm with the majority of the smart TRV's closing down at 10pm. But the whole idea of the system is to keep the CH early morning to night with the TRV's making the setup of each individual room much more flexible. It works well .... apart from this problem