Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Water pipes buried under floor advice needed in the UK Plumbers Forums area at Plumbers Forums

Messages
8
Hello, I hope someone can help me. I'm in England. I would like to know if it's okay to bury copper water pipes under a concrete floor. I've tried to look up the regs but's it's like double dutch to me. The pipes will be wrapped in hessian, overlaid with PIR insulation and then screed. I don't want to step on the plumbers toes but this doesn't seem a good idea. If I have a leak I will have to dig up the whole floor. Is there a better way to do this? There are meters of pipes going to be lying under my floors so I want to make sure they're protected as much as possible. Thanks for your time.
 
Can I ask why / do they need to be in the floor normally in the floor space above and drops down etc ?
 
Can I ask why / do they need to be in the floor normally in the floor space above and drops down etc ?
I don't see why they need to be put there but the plumber chose to put them there without any discussion. We have built an extension with underfloor heating in a large area so some of the hot water pipes will be lying under the underfloor heating. The cold mains supply runs near the edge of the room under kitchen units. The plumber is sub-contracted by the builder so I don't know him at all. What questions should I ask given they don't like me asking anything? It's all supposed to be to Building Regs standards.
 
I’m guessing it’s easiest for him you want them cleaning of flux eg hot soapy water and a green scouring pad every joint and then waterproof gaffa tape the lot and then 19mm insulation over the lot and joints water proof gaffa tap as well it’s given half a chance then
 
I’m guessing it’s easiest for him you want them cleaning of flux eg hot soapy water and a green scouring pad every joint and then waterproof gaffa tape the lot and then 19mm insulation over the lot and joints water proof gaffa tap as well it’s given half a chance then
Thanks very much for your advice. the pipes have been laid on sub floor like in the photo so will be a real pain to wrap tape around. What can I say to the plumber to get him to listen? He thinks it's fine. Is there anything in the regs?
 

Attachments

  • DE84F202-ABC5-4B60-B278-2A59FC1F824F.png
    DE84F202-ABC5-4B60-B278-2A59FC1F824F.png
    3.2 MB · Views: 35
Is that bare copper on show ?
 
See the above wras guidelines
 
Thanks very much for your advice. the pipes have been laid on sub floor like in the photo so will be a real pain to wrap tape around. What can I say to the plumber to get him to listen? He thinks it's fine. Is there anything in the regs?
I wouldn't be happy with bare copper laid directly on the slab , it needs to be pressure tested if there are soldered joints ? and be protected from unforseen damage before any floor insulation is fitted, there are better options in my opinion continuous plastic coated soft copper on a roll or Hep 2o in a conduit system would be better using a manifolded system you can avoid any joints under your floor slab . Kop
 
I can’t remember the distance off the top of my head but I’m pretty sure pipes need to be a minimum distance away from the edge of the screed (maybe 150mm).

They should also be above the dpm and insulation. And I think the minimum screed depth above the pipes is 50mm.

Also, one of those pipes is labelled gas, that can’t go in how it is. It can’t just be wrapped. It either needs to go in a purpose built open ended conduit or installed with factory pre sleeved copper pipe.

Lots of wrong here.
 
Very poor in all honesty🙁 it's not hard to make such a better job of the pipework it would be better run on top of the insulation wrapping in hairfelt by 50 % , gas pipework should not go under the damp proof membrane and insulation it needs to be above my go to product is Gastite pipe flexible stainless steel piping with a manufactured protective sleeve which can be buried in screed or sunk into the insulation prior to laying the screed . Kop
 
Very poor in all honesty🙁 it's not hard to make such a better job of the pipework it would be better run on top of the insulation wrapping in hairfelt by 50 % , gas pipework should not go under the damp proof membrane and insulation it needs to be above my go to product is Gastite pipe flexible stainless steel piping with a manufactured protective sleeve which can be buried in screed or sunk into the insulation prior to laying the screed . Kop
Thanks for this. The plumber is gas safe registered which makes it even more concerning. We are going to get someone in the check it and rectify urgently before the screed goes down. Thanks everyone for all your advice.
 

Similar plumbing topics

  • Question
Hello, I am just catching up on some threads...
Replies
1
Views
551
T
  • Question
Thank you. Good to hear this from someone who...
Replies
5
Views
2K
TAGolko
T
  • Question
I really appreciate the comments and advice...
Replies
8
Views
661
  • Question
Hi, the problems been ongoing since we moved...
Replies
4
Views
884
  • Question
Any thoughts on this bottle gully arrangement?
Replies
6
Views
626
Back
Top