Good question. It was for a fix on a 9 yr-old boiler. Was chasing a tw@t of a fault, intermittent dhw (once every few weeks, boiler overtemped), even after every one of the usual dhw suspects had been tested or replaced. Reset fine every time, no fault codes & was never there when I tested it:- normal operation, performance mode, min mode, dhw on/off loads of times, service menu-ntc sensors, dhw flow rates, fan rpm, fan pressure, everything tested fine.
The only thing left was the pump, but it was less than a yr old (I had fitted it) & ch worked great, all the time. Got the fault to occur just once while testing, and could hear a very quiet (almost imperceptible) ticking noise from the pump.Just out of desperation I swapped out the pump electronics module from a seized pump and now all seems well for over a month.
I did notice that when the boiler was initially powered up & the pump runs for a couple of seconds during the start-up sequence, with the old module fitted the pump only ran once every 3-4 power-ups, with the replacement module it ran the pump every time.
Throughout all this time (6 months), there was never a problem with the CH function, just on DHW.
This one had me pulling my hair out & bacame my nemesis. If the fault ever comes back again, I think it's time to recommend a new boiler.... Or I might just be away on holiday, permanently!!