There's no such thing as a 30m2 pack... As ... It all depends upon the heat loss of the room, the designed flow temperature, and possibly the heat source.
Ask him for the heat loss calculations.
Old leaky buildings like the one I surveyed today, 150W/m2 house size 80m2 heat load 12kW
Then there's the new build we're working on 450m2 , 26W/m2 Heat load 12kW
The design and installations are completely different... (the first isn't suitable for ufh, the second we have to cool the house in the summer...)
What length of pipe did he install, how many loops, serpentine or snail,
What was the designed flow temperature for the underfloor heating?
Has he connected the flow and return the wrong way round?
Is the TMV on the manifold configured correctly?
Does the underfloor heating have it's own circulation pump?
Did he just tap off the existing heating circuits?
Are there in screed stats or just air stats?