Hi

I live in Housing Association property and 10 years ago, they installed a wet room for me. They installed an electric shower and there is a water sensor on my cold feed, to kick in the shower waste pump.

Over the years, the water flow on the shower has deteriorated, and they would not install a new shower for me, so I decided to install a mixer shower. The electric one (for the time being) is still installed and working.

The problem I have is that the water waste pump is not working when I use the mixer shower. I have taken the cold feed for the mixer shower after the water sensor, so cannot see any logical reason why the waste pump will not kick in. The waste pump works fine on the electric shower.

Just wondering if anyone would have any suggestions.
 
Hello,

It depends on if the flow sensor is connected to your pump via the shower, sometimes called a whale instantmatch pump. Have you since tried the electric shower to see if that still pumps? If it doesn’t it could be the flow sensor or even the transformer bit could be from your shower, it’s been a while since I worked on them.
Also you may need an additional flow sensor as the pump may struggle with the demand as it’s designed to pump at a certain flow rate.
 
Upvote 0
Thanks for your response. The waterflow sensor is connected directly to the pump. There are only two wires coming out of the pump. Twin and Earth (for the power) which is connected via my extractor fan and the water flow sensor.

The pump works fine if I turn the electric shower on.
 
Upvote 0
Electric shower still installed ?

If so how have you connected the flow switch to the new mixer shower ?
 
Upvote 0
Yes, the electric is still installed and working.

I just tapped in to the cold water feed after the water sensor.

When I can work out what is happening with the sensor, I will just cap off when I removed the electric piping.

14icwso.jpg
 
Last edited:
Upvote 0
whats with the pressure reducing valve? below the white overflow pipe
 
Upvote 0
I thought that was a filter. That pipe carries on to the electric shower.

Thats maybe why your having bad pressure on your elec shower

Turn the mixer shower fully cold eg lowest temp does the pump kick in
 
Upvote 0
Got to the bottom of it. If I turn my combi water temperature to max and set the shower to cold, the pump kicks in.

I will move the sensor over to the hot pipe, and try and order another sensor for the cold pipe.

i would try moving the sensor to the hot pipe as this uses more water than the cold

as it unit might not support two sensors etc
 
Upvote 0
I thought it was, I was mistaken. It was Hydro Logic Dual (who no longer seem to be in the residential pump business).

Anyway playing with the jumper settings, I have managed to increase the flow, put the sensor on the hot water and everything is working.

Thanks ago for all your help. Very much appreciated.
 
Upvote 0

Similar plumbing topics

  • Question
Mira 88 was another but I don't think it was...
Replies
2
Views
572
  • Question
Hi SI......is the shower on the same floor as...
Replies
12
Views
366
A
  • Question
Stnd wrong pump for a high pressure shower...
Replies
1
Views
735
  • Question
We have a pumped shower with a...
Replies
0
Views
477
Back
Top