What might make combi produce low dhw flow? | Plumbing Jobs | The Job-board | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss What might make combi produce low dhw flow? in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

WaterTight

Esteemed
Plumber
Subscribed
Messages
5,433
Mum just moved into new place. I am not GSR but can do rest plumbing. She has a logic 24 combi. Hot at all outlets flow resembles what you might get from a fortic in a flat. Boiler fires fine, water gets hot, just poor flow. Cold is fine/normal. Is this something a gas safe guy will have to investigate/fix or something I can look at?

Thanks
 
24 kw is about 9 litres a min.
Might look poor through a bath tap. Measure flow into a jug and time it. That will give you litres a minute. Bet it's not far off.
 
It's the lowest flow I've ever seen on a combi and have worked on taps on hundreds of combis. I would guess from checking it out it would be maybe 4 litres a min tops.
 
tbh she's not fussed but doesn't seem right to me and if it was a reasonably simple fix, even if needing a gas safe chap I'd recommend it for her. Just want an idea.
 
dont know if they have but check the strainer
 
Are flow restrictors fitted?
Could be the strainer partially blocked?
 
As said, not GSR so no knowledge about boiler parts/workings.

Would the strainer be this thing on the right? And how do I 'check' it?

spu3rp.jpg


It is a hard water area yeah. Not sure if flow restrictors are fitted or where I would check that, unless you mean at/on the taps?
 
The strainer is inside the boiler
Flow restrictors may be inside the isolation valves for each tap
 
Probably scaled up heat exchanger
That's where I was heading, could even be a scaled up inline scale reducer. The long chrome thing on the left. Or has someone part turned off the flow valve to the boiler?
 
Would a scaled up inline scale reducer just reduce hot flow, normally? I can check that one.

I can't do anything within boiler as not GSR.

Will check there aren't flow reducer on iso's to taps.

Given the boiler then if I managed to increase the flow would it suddenly struggle to keep water hot if taps turned on too much? At the moment water nice and hot. As I said my mum isn't too bothered and don't want to swap one problem for another but would like to increase her hot flow if I could, mainly because filling a bath would currently take a month.
 
WT , yep bin the scale reducer ( at least for now) , only other thing is the flow turbine in the boiler could be prone to crud , but you would need to go in the boiler for that .
 
Divide the Kw rating of boiler by 3 to get expected flow in litres/min.
24Kw should give 8 litres/min. If you can confirm cold water flow to boiler exceeds 8 litres/min then problem is most likely scaled up domestic hot water heat X. Could be faulty diverter valve but in hard water area any heatX more than 6 years old is worth replacing even if problem is elsewhere. Need to be GSR.
 
I had one with a similar problem i had to strip down the whole hyroblock and clean it out as it had not been used for over a year there was a obstruction once removed all was ok 9-10 litres a minute regards kop
 
Status
Not open for further replies.

Similar plumbing topics

Di do not know much about this heating stuff...
Replies
16
Views
2K
Hi John, This was actually a house I'm...
Replies
6
Views
1K
A
  • Question
Our building has a boiler that provides both...
Replies
0
Views
751
arkay-eff
A
It won't work I wouldn't expect. NRV's...
Replies
3
Views
60
Back
Top