moogwai

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,343
Got pulled up by a manager the other day as on a job i diagnosed a glowworm ultimate 50bf with a faulty gas valve.
Now the room the boiler was installed in had a wc and a basin in and it never crossed my mind that this room was a compartment and my manager is calling me in as he says i shouldve ar'd the boiler as the room had no additional ventilation.
The room is also outside in a covered walk way at the side of a house
Just wanted to know what you guys think.
 
To me if you can open the door walk in and close it behind you and still have room to work on the boiler its a room not a compartment
 
It's the qubic size but I can't remember what it is is have o look it up someone will know
 
That was quick there lol , got answer I suspect hey ment m3
 
Last edited by a moderator:
Is the flue position correct ? Not into a carport ect ?

Sounds very harsh to Ar for that.

It must be a very big compartment to get a wc and sink in it,
 
if you can fit a table and a chair in there its not a compartment
 
I would have thought it was a room you where in, not a compartment. Plus I think it's harsh to AR. it'd have thought NCS would be ok if they wanted to class this space as a compartment, due to the size.

Hows it going at the AA anyway mate?
 
Yeah flue is fine....on an outside wall into their garden....as previously said i think to ar the boiler it would be harsh but my manager obviously thinks different. Have a meeting with him on wednesday...will let u know what he says. Thanks for yer thoughts lads.
 
corgi man told me years ago if you can get in with the boiler and shut the door behind you its a room although i have seen a cubic measurement mentioned on here as nowdays no one is allowed to make a judgement if there is a toilet and basin in there as well as a boiler its almost certainly a room
i would get the definative answer monday morning from gas safe so as to be ready for the managers questions either way
 
Last edited:
Wouldit not be classed as a cloak room ? With it have facility's in
 
i would definitely argue that it is a cloak room regardless of size im sure if it was your managers house and he was selling it he would describe it as a cloak ROOM
 
Check it out:

From current BS 6798:2009
Specification for installation and maintenance of gas-fired boilers of rated input not exceeding 70 kW net

5.3.2 Boiler compartment installations
5.3.2.1
The boiler compartment shall be a fixed rigid structure, the internal surfaces of which conform to the boiler installation instructions.

COMMENTARY AND RECOMMENDATIONS ON 5.3.2.1
If the boiler manufacturer’s installation instructions do not give specific advice, then any internal surface of the boiler compartment which is of combustible material should either be at least 75 mm from any part of the boiler or should be lined with non-combustible material. Methods of determining whether a material can be described as combustible or non-combustible are given in BS 476-22. For further advice, see HSE publication, Safety in the installation and use of gas systems and appliances [14].
5.3.2.2 The compartment shall permit access for inspection and servicing of the boiler and any ancillary equipment. A notice shall be fixed in a prominent position within the compartment to warn against its use as a storage cupboard. The compartment shall be fitted with a door that will permit withdrawal of the boiler and any ancillary equipment.


Your boiler is RS, you are good to go.
 
Last edited:
I would have thought it was a room you where in, not a compartment. Plus I think it's harsh to AR. it'd have thought NCS would be ok if they wanted to class this space as a compartment, due to the size.

Hows it going at the AA anyway mate?

AA is ok Tom......would much rather be working for myself though....bleedin phone aint stopped ringing since ive been there
 
In case of an Open-flued appliance (moogwai, your boiler is RS):

From current BS 5440-2:2009
Flueing and ventilation for gas appliances of rated input not exceeding 70 kW net
(1st, 2nd and 3rd family gases) –
Part 2: Specification for the installation and maintenance of ventilation provision for gas appliances

6.3.2 Open-flued appliance installed in an appliance compartment
...
...

COMMENTARY ON 6.3.2.1
The purpose of the air vents in an appliance compartment is to provide air for combustion, correct operation of the flue and appliance compartment cooling. It should be noted that small appliance compartments are susceptible to vitiation caused by down-draught and so great care should be taken to ensure that the ventilation provision conforms to 6.3.2 or the manufacturer’s instructions.

Small rooms, such as individual WCs, cloakrooms, understair spaces, are not normally considered appliance compartments. However, like small appliance compartments, they are susceptible to vitiation caused by down-draught. For this reason, and in cases where the heat loss from the appliance could lead to high ambient temperatures, appliance compartment ventilation should be considered.


Your boss could have a case here.
 
In case of an Open-flued appliance (moogwai, your boiler is RS):

From current BS 5440-2:2009
Flueing and ventilation for gas appliances of rated input not exceeding 70 kW net
(1st, 2nd and 3rd family gases) –
Part 2: Specification for the installation and maintenance of ventilation provision for gas appliances

6.3.2 Open-flued appliance installed in an appliance compartment
...
...

COMMENTARY ON 6.3.2.1
The purpose of the air vents in an appliance compartment is to provide air for combustion, correct operation of the flue and appliance compartment cooling. It should be noted that small appliance compartments are susceptible to vitiation caused by down-draught and so great care should be taken to ensure that the ventilation provision conforms to 6.3.2 or the manufacturer’s instructions.

Small rooms, such as individual WCs, cloakrooms, understair spaces, are not normally considered appliance compartments. However, like small appliance compartments, they are susceptible to vitiation caused by down-draught. For this reason, and in cases where the heat loss from the appliance could lead to high ambient temperatures, appliance compartment ventilation should be considered.


Your boss could have a case here.

awww....crap.
 
Looks like it can be much less than 5m[SUP]3[/SUP]. Cos, accordingly to the BS, you only need 75mm clearance around the boiler.
 
Status
Not open for further replies.

Similar plumbing topics

If the pump is on the ground floor open any...
2
Replies
47
Views
4K
  • Question
Hi. Sorry if I missed it - did it get resolved...
Replies
5
Views
9K
There's nothing wrong with external boilers...
Replies
4
Views
2K
R
  • Locked
Hey all, apologies for the long post: I've...
Replies
0
Views
4K
richardc1983
R
L
  • Question
Thanks for replies.. So the hot water comes...
Replies
13
Views
7K
leeroy_25
L
Back
Top