Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss where is the condensate pipe? in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
3
I have a worster bosch combi boiler.
When I just use hot water everything is fine. If I turn the central heating on the boiler bubbles like crazy and tries to light with a booming noise.
It then fails and turns on the reset.
I have searched through various areas including this site and come to the conclusion the condensate is blocked.
Could this be the white plastic pipe that comes out of the bottom of the boiler and goes out through the wall?
I can't separate the joints, I assume it has been glued together.
It is possible it is frozen just outside the house.
If it is this pipe might just pulling it apart solve the problem and let the condensate go into a bowl in the room?
 
Too late I have managed to get the pipe off the bottom of the small tank, there was a small spray of water and now the system is working perfectly. I just have to, somehow, clear the pipe. I think the best way as It goes through a few bends is to cut it just inside the wall and clear it then get a double female for the plastic pipe.
 
Too late I have managed to get the pipe off the bottom of the small tank, there was a small spray of water and now the system is working perfectly. I just have to, somehow, clear the pipe. I think the best way as It goes through a few bends is to cut it just inside the wall and clear it then get a double female for the plastic pipe.
And now you have the possibility of carbon monoxide entering the property from the boilers condense trap. Please turn the boiler off and get an engineer out to make sure that it is done properly.
 
Status
Not open for further replies.

Similar plumbing topics

https://hhic.org.uk/uploads/5BD6D5A19764A.pdf...
Replies
19
Views
1K
Just to round this off with what I found here...
Replies
5
Views
626
  • Question
Thanks for the tip. I have an outside tap so...
Replies
7
Views
419
  • Solved
Thanks for the comments fowlerboi. Like you I...