You need thre timers - 1 for each of the CH Zones, and one for the DHW.
If you go with the CM927's with BDR91's you need a ST9100C for the DHW (You have time control for each CH zone on the CM927's) This is probably your best simple solution using Honeywell. Better would be Honeywell Evohome.
If you go with DT92E's you have no time control on the CH, so you now need a ST9500C for the 2 heating zones plus a ST9100C for the DHW.
Ignore the Honeywell wiring guides as they don't cover these configurations.
It's very simple you have and S-Plan system with DHW and 2 CH zones.
There are other controllers out there that are hard wired three and four channel timers, and there is no reason why you can't use those for the timer(s) and the DT92E's for the temperature control. (
4 Zone Time Clock Programmer - Heatmiser TM4-TS ) Heatmiser do a lot of other stuff as well and if you talk to their technical team, they can give you great advice.- We use either Honeywell, Honeywell Evohome, Heatmiser, or Heatmiser Neo exclusively on all of our installations. So far we have yet to find an installation that has beaten us
- we even had one with Underfloor heating, 'normal' radiators, radiant panels and fan coil units all within the same property.
If you want out of the home (internet) control and you don't want to hardwire the room stats go for the Evohome system. if you are preapred to hardwire them go for the Heatmiser NEOStat
Whichever you choose, allow at least a day to wire it all up, test it and configure it