Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Why 2 double check valves on filling loop in the UK Plumbers Forums area at Plumbers Forums

G

Gary c

Hi, I have recently had a water board inspection
This is what the report said about the filling loop on our press unit for a biomass boiler….

There is quickfill pipework directly between the mains water supply and heating supply. This type of temporary connection is permitted under the water supply regulations however the following must be incorporated:
1. Double check valve are required on both upstream (mains side) and downstream (heating side) of the braided temperate hose 2. Remove flexible braided hose when not in Use

I understand you need a double check valve and removing the braided hose when not in use, but why 2 check valves?
 
How many kw is the biomass ?
 

Information on fluid categories if it helps.

Probably gone for the 2 x double check to protect the mains supply and risk of backflow as much as possible without slapping you with an RPZ install notice as you could technically just connect to the downstream side from another source if it didn't have the backflow protection on that as well.
 
The same could be said for a dcv failing tho
True, there is always the risk with CAT 3, but if the water undertaker has instructed it to be installed as long as you've followed instructions you are covered.

Even CAT 4 RPZs fail and as long as they are repaired/replaced within the undertakers guidance time period you are covered. Only true backflow protection is CAT 5 to be honest.
 
True, there is always the risk with CAT 3, but if the water undertaker has instructed it to be installed as long as you've followed instructions you are covered.

Even CAT 4 RPZs fail and as long as they are repaired/replaced within the undertakers guidance time period you are covered. Only true backflow protection is CAT 5 to be honest.

Another down side to rpz is the servicing
 

Similar plumbing topics

  • Question
They need to hold there g3 certificate eg...
Replies
4
Views
436
Thank you I presume there are no backflow...
Replies
4
Views
1K
  • Question
This issue arose about a year ago. Does anyone...
Replies
0
Views
653
  • Question
Brilliant, thanks for your help
Replies
5
Views
1K
C
  • Question
Is there a ball valve on the flexihoses? Might...
Replies
1
Views
852
Back
Top