Had a combi boiler installed, Power flush as well. but I have 1 stone cold radiator, all the rest through the house get piping hot, thermostat have been changed, inlet valve has been changed, water flows through the radiator, if youy try to bleed it it comes straight out. so no air in the system.
But the water is cold, won't get hot at all. Even had the radiator off the wall and blown through...

What else could it be?? Does anyone have any ideas??
 
You get water out of both rad valves?
what size pipe? 15mm or microbore? Was system properly balanced by installer?? Try closing all other rads does that rad warm??
 
if the pipes are mico/10mm and come down from above you may have a air lock,
turn off trv and lockshield and then open one into bucket till warm water comes out, then do same at other side, reconnect job done.
 