Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Wireless Boiler Controls - Are ESi any good in the Boilers area at Plumbers Forums

Messages
10
My daughter has recently moved into her first house which has a Worcester Greenstar 25Si Combi. It has an ESi ESRTP4RF Wireless Programmer/Thermostat fitted, but the wireless connection keeps dropping out.

Does anyone rate these units?

There seem to be plenty of DT20RF/LP20RF units up on ebay. Should I go for one of these instead or do people recommend something else?
 
try moving the prog closer to the reciever see if it still happens
 
ESi customer service are excellent I’d give them a call. Could just be a faulty unit
 
Not with thermostats as I’ve never had a problem with them but they were excellent replacing a faulty valve
 
Have you thought of getting the hive installed, sometimes they come with cracking deals with installation included

Yes, I've been looking at Hive as an option, but they have also have a new baby so they're a bit skint at the moment, and splashing out on boiler controls is not really their top priority, hence why I was looking on ebay for a cheap and simple alternative solution (DT20RF).

A hive single channel receiver, Programmer/thermostat and hive hub could be the wierdest christmas present they've ever had though!
 
Yup. Twice. I've read various posts about wireless units dropping out due to interference, but I've no idea how I would rule that in/out.

I fit Siemens and Honeywell, both recommend Alkaline batteries for signal strength, are you using them or cheap zinc ones? Had so many customers using zinc batteries. :(
 
My experience of ESI units is that they are robust and of a good quality. Their technical support team are (in my experience) very responsive.

The symptoms you describe are that of an incorrectly bound unit. Sometimes units have been reused and paired without the previous bindings having been properly cleared.

Clear the bindings, reset the units and rebind.
 
Yes. And because it looks like I could get one cheap on ebay! Is this a poor choice? I don't want to spend a lot of money only to find out we're no better off.
You will need a gas safe engineer still to fit it as you’ll need the old one unwiring and the case will need to come off the boiler
 
Is there any way of changing the frequency it operates on? I don't know the exact one you have but on a lot of them you can alter it by pulling some of the jumpers out and repairing, that might be worth a try if you can.
 

Similar plumbing topics

That is true - however with Vaillant...
Replies
4
Views
855
I will have to experiment like you said and...
Replies
6
Views
924
Its a Combi. Its a Worcester Bosch Greenstar...
Replies
8
Views
1K
Hi, From my experience, ESI controls are...
Replies
6
Views
2K
You need a GSRI to replace it sorry thats the...
Replies
4
Views
1K
Back
Top