Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Wiring help in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
B

Bhoydavid

Evening, looking for some wiring advice. Got a vokera mynute 15vhe heat only boiler. When I put the programmer (Horstmann 425 diadem) on for hw only the pump runs bringing the ch on. So basically I can't have hot water only. Anyone have any tips? There is no zone valves.
 
hot water is on gravity (no pump) pipe should be 28mm

heating is with pump on (hot water also)

needs updating tbh
 
hot water is on gravity (no pump) pipe should be 28mm

heating is with pump on (hot water also)

needs updating tbh
Ideally would've fitted zone valves or went to a combi but we are the pearl of the custard.


What hat I don't get though is how the ch comes on when the demand is only for hw. It's been wired the exact same as the old boiler.
 
Ideally would've fitted zone valves or went to a combi but we are the pearl of the custard.


What hat I don't get though is how the ch comes on when the demand is only for hw. It's been wired the exact same as the old boiler.

boiler would still come on but pump wouldnt so if you have wired the pump to the boiler both would
 
boiler would still come on but pump wouldnt so if you have wired the pump to the boiler both would
How will I fix this mess? I've spent about 6 hours trying various combinations and just praying:smilielol5:

Close to tears
 
How will I fix this mess? I've spent about 6 hours trying various combinations and just praying:smilielol5:

Close to tears

either update which i would go for (but you could just put a 2 port on the heating but i would go full hog)

hot water = just boiler coming on but have a feeling over heat thermo stat will kick in / no flow through boiler

heating = pump and boiler come on
 
Last edited:
Is this a new boiler? If so, how have oyu fitted on gravity?
 
Last edited:
Have you just fitted a new timer,
is it set to gravity hot/pumped ch.
Sounds like the h/w and ch are wired the wrong way
 
Sounds like installation fault...

No zone valves on a new boiler?? Rads will always get hot if there's no zone valves but the pump comes on!? The new boiler would not exactly work on gravity...
 
You shouldn't have installed it like that to be honest.

Under part L you need to provide independent time and temperature control to heating and hot water. Impossible with out zone valves.
 
Cheers. I wasn't aware of the issue of no zone valves. Arranged to go back and fit zone valves and get it zoned off.
 
Status
Not open for further replies.

Similar plumbing topics

S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
114
S
  • Question
I wish it were true, I wish I could say, That...
Replies
18
Views
2K
3 hw on 4 htg on 5 perm live
Replies
1
Views
1K
Thanks Shaun I will have a go at it on...
Replies
14
Views
2K
That is true - however with Vaillant...
Replies
4
Views
848
Back
Top