Wiring problem 2 zones pumps + salus it500 | UK Plumbers Forums | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Wiring problem 2 zones pumps + salus it500 in the UK Plumbers Forums area at Plumbers Forums

Messages
3
Hello!
Please help me!
I have a thermostat salus IT 500 and it300, Ariston Genus One 35kw and 2 pumps for 2 heating zones.
What I want: to independent control each zone, floor no1 and no2, with the pumps. When the temperature that I seted up reaches, the thermostat to command a pump to close the circuit.
Problem: I can't make the wiring system.
 
You will require two single Pole contactors

Simply

Lne to stat
From stat call goes to a1 on contactor a2 neutral from stat / same circuit
Then a perm live to one side of the contactor from the same circuit
The other side to the pump

Hope that makes sense
 
You will require two single Pole contactors

Simply

Lne to stat
From stat call goes to a1 on contactor a2 neutral from stat / same circuit
Then a perm live to one side of the contactor from the same circuit
The other side to the pump

Hope that makes sense

Screenshot_20181123-181622.png
 
Stat won't be rated for the pump amps so could blow / damage it
 

Similar plumbing topics

  • Question
I only have 1 UFH zone using 3 heads plus 2...
Replies
5
Views
831
T
  • Question
There is regular mechanical clicking and there...
Replies
2
Views
2K
Tractorman_
T
D
  • Question
Advice needed please: I have an UFH...
Replies
0
Views
1K
DIYTony
D
Either will be fine also your salus will fit...
Replies
4
Views
1K
  • Question
Thanks -thought that might be where I'd end...
2
Replies
27
Views
3K
Back
Top