Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester 15Ri intermittent fault. in the Plumbing Jobs | The Job-board area at Plumbers Forums

billski

Gas Engineer
Messages
88
Has any one got any ideas??
Greenstar 15Ri gas boiler. Works fine sometimes with out fault, but every now and again it just stops like it has no power. Blue light goes out and nothing happens, still have 240votls on the board. Light comes on, fan tries to run then light out and nothing, yet still have 240 volts.
New external timer has been fitted, new 3 port valve fitted, new PCB board and the black transformer box on the board fitted. Still has the same fault.
Checked all teminals and connections. Wiring all checked by an electrician and all seems fine. Worcester tell me if there is no blue light then there is no power to it, yet there is. They have suggested I do everything that I have but have no other ideas??
 
You checked the fused spur / switch isn't fecked ?
 
You checked the fused spur / switch isn't fecked ?
I haven't but believe the electrician has. The external pump doesn't stop running though and the timer doesn't go out. All connected to the spur. The spur does look quite old though.. I still get a constant reading of 240volts though at the boiler.
 
Very strange
 
Check your neutral to boiler, had similar a few weeks ago and found a nearly chewed through neutral (mice) giving an intermittent connection
Had 240v on live to boiler, but still wouldn't work without neutral
 
Just incase any one is interested. Finally managed figure out what was wrong with this boiler. Not only was the old pcb faulty but the new one I put is was also faulty! Bought another pcb and it's working perfectly. What a head ache that was trying figure it out.
 
Just incase any one is interested. Finally managed figure out what was wrong with this boiler. Not only was the old pcb faulty but the new one I put is was also faulty! Bought another pcb and it's working perfectly. What a head ache that was trying figure it out.

Just curious Billski as I've fitted a few of these, how old was the boiler and had it been looked after?
 
Yeah I got them to swap it as I use the same merchants all the time, so they're pretty good at taking stuff back. I learnt to buy things locally a long time ago when I fitted a PCB on a Glow Worm heat only boiler. The original PCB was blowing the fuse with a bang! Replaced the board, which was bloody expensive! 2 weeks later new board doing exactly the same thing.. Replaced it with another board and it was fine. That was 4 years ago and it's still working as it should. The supplier I was using then did huff a puff about swapping it and did try to fob me off with telling me I'd have to wait for a refund once Glow Worm had tested it. My contract was with the merchants not Glow Worm, so they should swap it straight away as it's not my problem.
 

Similar plumbing topics

Have you checked L-N ? 240 ?
Replies
1
Views
2K
Hi all. I hope you are well. Need some advice...
Replies
0
Views
525
J
Turned the system from hot water only, to hot...
Replies
0
Views
551
James Middleton
J
Get him to check electrodes
Replies
3
Views
895
Thanks I’ll get a new fan then. I literally...
Replies
3
Views
1K
Back
Top