Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester 24i SFR Combi boiler low presure in the Boilers area at Plumbers Forums

Status
Not open for further replies.
Messages
5
Boiler.JPG
Boiler 1.JPG
Boiler 2.JPG
Hi I had to vent radiator in bathroom, was heating only at the bottom, well, the pressure dropped, try to repressurise it and I can't see any valves or key valve or anything else, do I need engineer to do so or there is something to do to fill the sysytem? appreciate any help.
 
Last edited:
Any chance of a pic of the bottom/ underneath of the boiler ?
 
any chance there is a sliver braided hose to the left?

and pics didnt show up when i posted must of taken some time to load onto the server
 
Aren't the filling loops built in with the white keys on this model?

Edited as pictures only just popped up. Sorry
 
any chance there is a sliver braided hose to the left?

and pics didnt show up when i posted must of taken some time to load onto the server
No no silver or any other hose, also the domestic inlet and outlet goes directly into and from the heater, inlet has got I guess flow sensor and thats it, also I will check later behing washing machine there are pipes going into the boiler.
 
Just looked at the instructions. There will definitely be an external one on the system somewhere. Where is the boiler situated?
 
Just looked at the instructions. There will definitely be an external one on the system somewhere. Where is the boiler situated?
Hi, yes it is RSF the boiler is in kitchen close to sink where main water supply is, there is washing machine below, and supply pipes are behind, also all pipe work from and to boiler are going behind the cuppboard, it's buildin can't strip it off, I looked into the manual on worcester website and could not find this section, there was something about to call the installer, thgis what makes me wander, if I call for plumber, what's the chance this person can sort it out unless he well fit extra pipe with valves underneath, but how this been filled at firs place?
 
there should be a filling loop somewhere your best way if you can is to follow the mains cold pipework it should be somwhere along that line
 
Chances are mate. That it will be inside a cupboard somewhere or behind the washing machine.
 
glade you found it, and thank you for updating us
 
Status
Not open for further replies.

Similar plumbing topics

System boilers have a pressurised heating...
Replies
1
Views
268
There is 6 pipes under the boiler and one goes...
Replies
19
Views
991
T
That would seem prudent, although I never see...
Replies
6
Views
902
Thank you for reply. I have isolated the noise...
Replies
2
Views
374
Thanks, so i need another one?...otherwise the...
Replies
2
Views
650
Back
Top