one difficult job, the boiler will work for hot water and heating for around 30mins, then boiler goes out followed by hot water light flashing rapidly. the manual says air flow fault, colleague has replaced air pressure switch, i ve checked all air tubes for splits and blockages, replaced fan still get the fault. checked both thermistors and resistance o.k for temp. rang worcester not very helpful said replace p.c.b luckily had one on van swapped it but made no difference, checked electrode and flame rectification gaps o.k. ckecked gas valve max and min o.k. flue is horizontal is on first floor. after couple mins boiler will come back on again on its own.
anyone else had this problem?