Rckape
I've replaced the old gas valve on the above for the new sit valve. The boiler was firing on on the old one but the FGA reading were way out.
I've followed all the instructions on setting the high and low for the size of boiler.
It's now not firing. On call for heat I get 35v at the molex connectors for around 2-3 seconds. For the same period of time I get a pressure drop on the gas inlet test point.
I get a spark on the igniter at the pcb and at the end of the leads and still no ignition.
The only thing I can think is that I've been setting the min/max incorrectly. The solenoid only opening for a 2-3 seconds is bugging me, I don't know how long they open when all is well.
I even refitted the old gas valve to check and it did exactly the same.
Am I missing something basic?