Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester 30si hot water fault. in the Bathroom Advice area at Plumbers Forums

billski

Gas Engineer
Messages
88
Worcester 30si combi boiler, hot water doesn't stay hot. Boiler stays lit & seems to be happy, diverter valve working as it should, central heating works fine. Flow rate at the tap is above what it should be, but it has worked fine for 9 years. Replaced tem sensor, even though it tested out okay on my meter, no change. Next I'm thinking plate to plate heat exchanger, but the flow rate doesn't seem restricted and it's not cutting out. Could the flow turbine be faulty? If so can I test in?
Appreciate your thoughts.
 
Plate

Test the temp drop across the plate both end eg both heating and hot water sides of the plate
 
Should the temp drop be minimal?
And could it still be the flow turbine?

Should be decent eg flow 70 return around 20 is depending on hot water eg 50dc

No as it's staying fired
 
Yes with the flow rate being good hot water side so not block with lime scale etc
 

Similar plumbing topics

That’s normal tbh won’t go into max burn on ch
Replies
3
Views
861
  • Question
Morning, he took it out from where it was...
Replies
11
Views
818
Are you Gas Safe Registered? If not please...
Replies
2
Views
536
J
  • Question
Does it have the 3 contacts above where the...
Replies
1
Views
1K
New flow sensor and we now have hot water.
Replies
5
Views
772
Back
Top