Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester 42CDi Gas Rate in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.

CES

Plumbers Arms member
Plumber
Gas Engineer
Messages
2,475
This is doing my head in, Im trying to calculate a new gas pipe run as the numpty who installed it used 22mm pipe on about a 25m run. So I've got the MI's out to check the gas rate, heat input etc and they say 4.4m[SUP]3[/SUP]/hr and max kw of 42.
Now this doesn't add up in my head as 4.4m[SUP]3[/SUP]/hr works out as 47kw and working back 42kw should give a gas rate of about 3.9m[SUP]3[/SUP]/hr.
Am I getting the early onset of dementia? or are the MI's wrong?
 
You don't suppose the boiler is a 42 kw output with a 47 kw input, 4.4m3/hr
 
your right worcester goes quote 42 kw & 4.4 m3/hr gas rate for a 42 cdi,
but the 42kw is heat input [net], you need to change net to gross, ie 42 x 1.11 = 46.62

4.4 x 38.6
3.6 = 47 kw boiler efficiency = 42 divided by 46.62 = 90%


as for pipe size, you can run 28mm around 30m [for 4.4m3/hr ], so for a 25m run and allowing for a few bends and no other appliances, you might just get away with 28mm pipe, realistically your gonna need some 35mm pipe if there's other appliances.
 
Cheers, it says max rated heat input as 42 and max rated heat output as 42, I should have clicked. It would help if they were a bit clearer with their MI's though I thought I was losing it.
 
Status
Not open for further replies.

Similar plumbing topics

If you have the right temperature rise for the...
Replies
10
Views
3K
No would expect 70 if the sensor is saying 75...
Replies
5
Views
4K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
857
HRP123
H
On the basis that one opinion is good but two...
2
Replies
25
Views
7K
Back
Top