Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester boiler needs refilling daily in the Boilers area at Plumbers Forums

Status
Not open for further replies.
P

proelitegas

Hi just got a customer complaining he is having to fill his boiler
Daily.When central heating is on pressure rise as normal on
Gauge but when heating is off pressure falls and discharge via blow
Off..I'm thinking expansion vessel needs recharging any other thoughts
Would be appreciated..thanx
 
absolutely worth checking the EV but to me it sounds more like the PRV is letting by as it's happening during the off, ergo cold, period
 
Any tips on checking the operation of the prv ???

not really a way of checking the operation as such, they're usually set at around 3 - 3 1/2 bar so if it went then the system for whatever reason got fairly high on pressure. The trouble is once they go very often they don't re-seat properly, there may be a bit of grit on the seating or the washer may have perished. Some can be dismantled and cleaned but most techs don't bother they just re-new.
 
proelitegas .. filling daily with no wet carpets or saggin ceilings usually means exp vessel lost charge and 9/10 prv taken out! As for checking prv I wouldn't recommend it ... In my experience once they've been pasing they rarely sit sealed again! :)
 
Thanx everyone will check e v and if need be recharge see how
That goes...Thanx again
 
proelitegas .. filling daily with no wet carpets or saggin ceilings usually means exp vessel lost charge and 9/10 prv taken out! As for checking prv I wouldn't recommend it ... In my experience once they've been pasing they rarely sit sealed again! :)

agree +1
 
Plus plus 2
 
I had an ecotec last week that had blown it's internal rubber flow pipe (the merchants told me that they're selling at least 3 adjustable hard pipe replacements every week, apparently it's a design fault) anyway, the over-pressure on this particular boiler was caused by a faulty internal filling loop, in this case there was nothing wrong with the prv or ev, not saying that this is your problem but it maybe worth a quick check
 
Status
Not open for further replies.

Similar plumbing topics

M
Isolate and drain boiler. Pump up expansion...
Replies
1
Views
741
That means you have a leak as the system...
Replies
9
Views
829
    • Like
Of course, missed that off the first message...
Replies
2
Views
664
Thank you for the detailed and considered...
Replies
14
Views
1K
Gut feeling is PCB Time for someone...
Replies
13
Views
2K
Back
Top