C
CraigT
Hi. I've got a Worcester Bosch Heatslave 20/25 oil fired boiler and the burner has stopped igniting.
I have done a fair amount of fault finding and this is what I have found:
If there is a demand from either the hot water, or the heating the burner blower starts, but there is no ignition. It also just continues to run like this; there's no lock-out.
There is oil getting to the pump, but no oil getting to the nozzle (checked by opening the oil pressure blank on the line from the pump).
When there is a demand for the boiler to ignite the oil pump solenoid is only receiving 131v, which I assume is not enough for it to open. The resistance of the solenoid coil is 2300 ohms. If I temporarily wire a fused 240v input to the solenoid terminals it operates correctly and the boiler ignites & runs fine.
Is this pointing to a faulty control box, or is there something else in the electrical circuit that might be preventing the solenoid from being actuated?
I believe that the part number for the control box is 87161200970. A search for this shows a new one to be about £200, however a search for a TF832.3 control box (as printed on the front) has led me to this (sorry, won't let me post url's): heatingsparescentre dot co dot uk/satronic-c23/satronic-control-boxes-and-accessories-c2970/satronic-honeywell-tf8323-oil-burner-control-box-p22492 , which is only £41. Is there a difference, or is this just a brand name thing?!
Thanks,
Craig
I have done a fair amount of fault finding and this is what I have found:
If there is a demand from either the hot water, or the heating the burner blower starts, but there is no ignition. It also just continues to run like this; there's no lock-out.
There is oil getting to the pump, but no oil getting to the nozzle (checked by opening the oil pressure blank on the line from the pump).
When there is a demand for the boiler to ignite the oil pump solenoid is only receiving 131v, which I assume is not enough for it to open. The resistance of the solenoid coil is 2300 ohms. If I temporarily wire a fused 240v input to the solenoid terminals it operates correctly and the boiler ignites & runs fine.
Is this pointing to a faulty control box, or is there something else in the electrical circuit that might be preventing the solenoid from being actuated?
I believe that the part number for the control box is 87161200970. A search for this shows a new one to be about £200, however a search for a TF832.3 control box (as printed on the front) has led me to this (sorry, won't let me post url's): heatingsparescentre dot co dot uk/satronic-c23/satronic-control-boxes-and-accessories-c2970/satronic-honeywell-tf8323-oil-burner-control-box-p22492 , which is only £41. Is there a difference, or is this just a brand name thing?!
Thanks,