Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss worcester bosh greenstar ri wiring in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

g60rge

Gas Engineer
Messages
94
hey guys, just been to quote for a job to replace the wiring center/programmer along with fitting a new greenstar ri.

just researching the wiring as i only really fit combis


ive noticed i need to wire the pump direct to the boiler for the pump overun - got that bit

in the boiler we have a LNE in and a LNE out - whats the out for? >when there is no spur near the wiring center?

i have a spur available at the wiring center, does this mean i dont need to use the out as i can run LNE from the spur to the wiring center then to the boiler in section

not forgetting switch live from the wiring center to the boiler

let me know if this doesnt make sense

thanks
 
For an Ri you'll need a 5 core
Permanent live, neutral & earth, plus a pump live & switch live...
A lot of the Worcesters have live to wiring centre etc but you don't need to do it that way...
 
yes as gas safe said the boiler will require mains power

Mains power 230v connection fused 3 amp (ST1):
– Connect LIVE wire to terminal (L)
– Connect NEUTRAL wire to the terminal (N)
– Connect EARTH wire to earth bracket

External Pump (to pump)(ST2):
– Connect LIVE wire to terminal (Lp)
– Connect EARTH wire to earth bracket

Boiler Demand (ST2):
– Connect SWITCHED LIVE wire to terminal (LR)

and then wire it like normal in the wiring center minus the live for the pump as that will be coming from the boiler
 
Last edited:
Status
Not open for further replies.

Similar plumbing topics

Is there any delay when you manually overide...
Replies
8
Views
780
Finally got an update from him. He cant do the...
Replies
2
Views
796
Thanks for the input on this, much...
Replies
4
Views
873
Could be right above the boiler pipework or...
Replies
3
Views
565
Back
Top