Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester Danesmore Oil boiler won't fire up after draining system to remove radiator in the Boilers area at Plumbers Forums

Status
Not open for further replies.
R

rico260z

Hi, after draining and refilling my system (to replace a radiator) my boiler no longer fires up but it DOESN'T lockout either. When I turn the power back on it sounds as if it's starting up (fuel pump etc starts making a noise) but don't hear it try to ignite and then it just sits there doing nothing with the on led's lit on the control panel. Think the boiler is a 15/19 model. Nothing was touched on the oil side of things so can only assume there is airlock somewhere but I bled the 3 bleed screws I could see in the boiler itself and the pump. Anyone any ideas what I've done wrong?? thanks
 
Re: Worcester Danesmore Oil boiler won't fire up after draining system to remove radi

Is there any heat at all in the boiler?
Tried the over heat reset on the under side of the main control panel
 
Re: Worcester Danesmore Oil boiler won't fire up after draining system to remove radi

Is there any heat at all in the boiler?
Tried the over heat reset on the under side of the main control panel

No the boiler doesn't have any heat at all as it doens't fire up at all when turned on. Is the overheat reset different from the reset but that you press when it locks out due to low pressure or if there's problem with the oil? If so I'll have look for that tonite then
 
Re: Worcester Danesmore Oil boiler won't fire up after draining system to remove radi

Its been two weeks, get an engineer before it starts to get cold and our availability decreases :)
 
Re: Worcester Danesmore Oil boiler won't fire up after draining system to remove radi

Its been two weeks, get an engineer before it starts to get cold and our availability decreases :)

Found the overheat reset and once I pressed that the boiler locked out and the usual lockout reset button lit up. after 5 mins I pressed that and happily the boiler fired up and seems to be fine now.
 
Status
Not open for further replies.

Similar plumbing topics

Z
Need more details. What boiler, what burner...
Replies
1
Views
828
hi, no current pipework in concrete i believe...
Replies
7
Views
1K
Was the oil pressure checked before replacing...
Replies
1
Views
923
Turned out to be a dirty flame eye inside the...
Replies
8
Views
703
Back
Top