I had a call out to a radiator leaking and boiler now not working so popped out,
Rad had a sweat from it which is fine boiler not working went to look at it nice EA fault asked how long it was like this oo 2/3 days (away to F***) anyway check the condy trap which was chocked but not blocking into the block, cleaned it etc checked flue all fine when called for demand boiler goes into its ignition sequence but does not light, fan sounds slow but am not a worcester expert checked the inlet pressure which was fine 22mb cracked the top nut on the gas valve could feel the fan trying to stuck the gas but no gas passin the valve, normally i would of got my multi meter out but i was mega hacked off because i got called out at 5.30 to a massive leak and the boiler was knacked
I am going to pop up tomorrow any thoughts about the above its a heat only worcester greenstar 18 heat only.
Steven
Rad had a sweat from it which is fine boiler not working went to look at it nice EA fault asked how long it was like this oo 2/3 days (away to F***) anyway check the condy trap which was chocked but not blocking into the block, cleaned it etc checked flue all fine when called for demand boiler goes into its ignition sequence but does not light, fan sounds slow but am not a worcester expert checked the inlet pressure which was fine 22mb cracked the top nut on the gas valve could feel the fan trying to stuck the gas but no gas passin the valve, normally i would of got my multi meter out but i was mega hacked off because i got called out at 5.30 to a massive leak and the boiler was knacked