I’m having a bit of a fight with a surveyor regarding flue clearances next to extractor vents, he is saying as long as it’s got flaps on the vent you can be as close as you want to it, I’ve told him it’s either 300mm or 150mm with plume kit directed at least 300mm away from vent..
the surveyor is having none of it, I contract for a heating company and if the surveyors sell the job wrong they get penalties,
He says he got a technical bulletin from Worcester stating as long as there is flaps on the vent the clearances don’t need to be followed, have any of you guys heard this because I know I haven’t, I would still class it as a opening to the building flaps or no flaps .