Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester Greenstar 25i head scratcher in the Plumbing Jobs | The Job-board area at Plumbers Forums

KingDoey

Plumbers Arms member
Plumber
Gas Engineer
Messages
288
evening all.

Called out to this boiler late last night. No HW.

Pressure was down so checked expansion vessel etc and topped up. Hot water demand fires boiler which lights and then quickly reaches 97 odd degrees before shutting down. Get an initial blast of hot water through the pipes then just goes cool.

Heating working fine. First thought was the diverter valve stuck but would expect to feel some heat on the primaries if that was the case.
Have changed a few plate hex on the 24i juniors in the past but in those cases the boiler was firing and producing lukewarm water, not overheating. So make me think not that.

Haven’t ever really had any probs with these boilers so does anyone with a bit of knowledge of them have any thoughts?

Boiler only three years old so will probably be a call to Worcester Monday morn to get them out under warranty.

Cheers
 
Last edited:
Check the pump. 9/10 over heat on hot water on these will be a weak pump.

Heating would be effected tho wouldn’t it ?

Op I would check the plate temps in and out could be blocked / restriction
 
Not really on hot water it will run 25kw on heating it will be 20kw or less. So as I've said 9/10 it will be a pump

But will be more resistance on the pump with heating on than hot water
 
Have you had the boiler in max fire mode (chimney sweep/service mode) on ch and testpost-1054067.rature rises on that?

Screwdriver check through pump bleed point?

If pump is fine on checks and doesn't rise excessively on ch demand then likely to be plate heat exchanger.

Ive had loads of em, and also there's been a fair few similar faults described on this forum.

Good Post to read which sounds similar is this

https://www.ukplumbersforums.co.uk/threads/worcester-over-heat-on-dhw.108291/page-2#post-1054067

Alot of back and forth but ended up being the plate heat exchanger and was solved using the f5/f3 cleaning method.
 

Similar plumbing topics

There is 6 pipes under the boiler and one goes...
Replies
19
Views
970
Yes that’s not normal best get an heating...
Replies
1
Views
2K
You want the lowest of ranges 1-4 that gives...
Replies
3
Views
7K
You could try a reset if that doesn’t work it...
Replies
5
Views
793
S
    • Like
Does it have pre-heat functions in the menu.?
Replies
5
Views
2K
Back
Top