Hi people, not sure if this is in the right section on the forum or not. I have come across a few Worcester Ri boilers recently on the housing association contract I work on.
One I went to a few weeks ago had been switched off due to high CO by the service engineer. I adjusted the gas valve as per the MI and it was fine. I have been to another one today and the CO was so high I think it has damaged the oxygen cell in my Sprint v2.
I have taken the boiler apart and someone has been f***ing around with it. God knows what they have been doing. The inspection and access cover is missing and has been covered by some closure plate tape. So first thing is, I'm turning it off. So I tried turning it on and it fired, but when it went to low fan speed, it cut out. So I checked the inlet pressure, 20mb.
The CO was through the roof. Tried turning the adjustment screw, but I can't actually check the CO2 because it's going far too high. Checked the premix pipe/duct and it looks fine. I took the burner and baffles out, cleaned them and they looked fine. I even cleaned out the condense trap. I rang and spoke to Worcester, but they said it was the heat exchanger needed cleaning. I have left it turned off for the moment as it was 6.30 tonight by the time I left. I have ordered the inspection cover too, but can anyone else shed any light on to what might be the problem? Might it just be out of adjustment on the gas valve? It was a Sigma valve with the adjustment on the valve itself as opposed to the adjustment on the gas pipe.
Thanks in advance, Arran.
One I went to a few weeks ago had been switched off due to high CO by the service engineer. I adjusted the gas valve as per the MI and it was fine. I have been to another one today and the CO was so high I think it has damaged the oxygen cell in my Sprint v2.
I have taken the boiler apart and someone has been f***ing around with it. God knows what they have been doing. The inspection and access cover is missing and has been covered by some closure plate tape. So first thing is, I'm turning it off. So I tried turning it on and it fired, but when it went to low fan speed, it cut out. So I checked the inlet pressure, 20mb.
The CO was through the roof. Tried turning the adjustment screw, but I can't actually check the CO2 because it's going far too high. Checked the premix pipe/duct and it looks fine. I took the burner and baffles out, cleaned them and they looked fine. I even cleaned out the condense trap. I rang and spoke to Worcester, but they said it was the heat exchanger needed cleaning. I have left it turned off for the moment as it was 6.30 tonight by the time I left. I have ordered the inspection cover too, but can anyone else shed any light on to what might be the problem? Might it just be out of adjustment on the gas valve? It was a Sigma valve with the adjustment on the valve itself as opposed to the adjustment on the gas pipe.
Thanks in advance, Arran.