Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester Heatslave 15/19 enquiry in the Plumbing Jobs | The Job-board area at Plumbers Forums

Messages
41
Hoping someone can answer this query. I am going to replace my expansion vessel on my Worcester Heatslave 15/19 oil fired boiler. I am fairly happy with most of the process my only query is within the instructions it says at the beginning to withdraw the boiler to prevent water ingress. But there is no further explaination as to how to do this. Advice would be appreciated.
 
I am assuming you mean it said to withdraw the BURNER?
That would be to prevent water falling on top of it and into electrics.
Problem is if you remove the burner out a bit, you will then be pulling on the oil hose connected to it and this can leak.
Also electrics need isolated.
Really a job for an oil service engineer to do. The new vessel gas precharge should be checked and kept in relation to system pressure.
It would be possible to remove the vessel carefully without pulling burner out, but would need old towels and plastic cover over burner area.
The old vessel will be extremely heavy if the membrane has ruptured and entire vessel full of water!
 
I am assuming you mean it said to withdraw the BURNER?
That would be to prevent water falling on top of it and into electrics.
Problem is if you remove the burner out a bit, you will then be pulling on the oil hose connected to it and this can leak.
Also electrics need isolated.
Really a job for an oil service engineer to do. The new vessel gas precharge should be checked and kept in relation to system pressure.
It would be possible to remove the vessel carefully without pulling burner out, but would need old towels and plastic cover over burner area.
The old vessel will be extremely heavy if the membrane has ruptured and entire vessel full of water!


Best- thanks for responding. I did mean withdraw the burner it was a typo.
 
Best- thanks for responding. I did mean withdraw the burner it was a typo.

Coincidently, today I serviced an oil boiler and moved the burner out and back in place carefully.
Then discovered the not particularly old oil hose had begun to leak and had to replace it
 

Similar plumbing topics

It doesn't have internal clock It doesn't...
Replies
2
Views
1K
Replies
2
Views
3K
B
  • Locked
Cheers Best, Would I just leave all the TRVs...
Replies
4
Views
4K
Balmeadie
B
B
  • Locked
As your under 10 posts there prob stuck in the...
Replies
4
Views
3K
Back
Top