This is more for information, since I have solved the problem today.
My Worcester Heatslave 20/25 Oil fired Combi would fire up correctly but after only a minute or so ( longer from cold ) would shut down and go to lockout. Turning down both HW & CH thermostat controls would put all the facia and control box lockout lights out, but unit would not restart until control box button pressed. Then it would fire up as normal run for a minute or so and lockout again etc etc.
Fault traced to coil on Danfoss BFP fuel pump. Presumably heating up and losing it's "grip" on the fuel valve. Before diagnosing this I was on the point of calling in engineer or just replacing control box so problem fixed for £35.00 !
Hope this helps someone out there !
My Worcester Heatslave 20/25 Oil fired Combi would fire up correctly but after only a minute or so ( longer from cold ) would shut down and go to lockout. Turning down both HW & CH thermostat controls would put all the facia and control box lockout lights out, but unit would not restart until control box button pressed. Then it would fire up as normal run for a minute or so and lockout again etc etc.