Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester Heatslave ii problem after oil ran out in the Boilers area at Plumbers Forums

Messages
5
We have an oil delivery booked for Friday but we ran out earlier today. We topped the tank with 150L from containers, bled the first boiler from the Allen key until the oil ran free and it fired up fine.

Did the same on the second one but that had an E9 over temp error. We reset the thermostat and it fired as well but clearly it got too hot. Now it runs but with lots of black smoke from the flu so turned it off. Is something clogged or worse? Thoughts... Thanks.
 
Have you checked the tank filter ?
 
Needs an oil engineer now. It's on the slippery slope to being sooted up. Needs a clean out, clean filters, new nozzle and combustion re setting with a glue gas analyser.
 
All fixed. Changing the nozzle and cleaning the pump filter got it burning correctly. It was well sooted up on the baffles and secondary heat exchanger but a good clean up later at it is perfect.
 