Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcseter CDi Conventional Boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
D

Danv44444

Hi Guys, I got called to look at the above boiler last week because the boiler would not stay ignited. The Flame kept fluctuating then eventually went to lockout. I phoned Worcester technical and tested evrything as they said but still couldnt find anything to fix it.

In the end the customer paid for worcster to come out and fix it for £250. The customer isnt very technical put said the worcester guy said it was something simple.

Have any of you guys ever come across this with worcesters before. I checked the gas valve, fan, Flue and cleaned the heat exchanger.

Any help for future reference would be appreicated
 
Hi Guys, I got called to look at the above boiler last week because the boiler would not stay ignited. The Flame kept fluctuating then eventually went to lockout. I phoned Worcester technical and tested evrything as they said but still couldnt find anything to fix it.

In the end the customer paid for worcster to come out and fix it for £250. The customer isnt very technical put said the worcester guy said it was something simple.

Have any of you guys ever come across this with worcesters before. I checked the gas valve, fan, Flue and cleaned the heat exchanger.

Any help for future reference would be appreicated

Hi pal
2 things condensate partial blockage.....but an FO code along with EA is more likely the electrodes, especially at 5 year old, on the old 40HE ( model before you could access a menu which indicated a converted micro amps value for 0 to 3, when a 0 or 1 was indicated electrodes needed a change)
CDi does not have this feature open to us, but Bosch engineers can see this value with the lap top.......part around £25 ish + vat, one thing ensure you get the modded part it has an additional metal flat gasket (heat shield) they also require changing more often on LPG.
 
Thanks Vern, I did take a look at the electrodes, they looked ok? is there anything i could have done to test them?.
 
Thanks Vern, I did take a look at the electrodes, they looked ok? is there anything i could have done to test them?.
Nah....it's metal fatigue, the ionisation probe is sometimes a giveaway, it becomes tapered and the end and sometimes green!
Did you set up high and low fire with an FGA.? 9.7% high and 9.1% low, if they go below 8.6% co2 on low fire with anything but a good electrode set they can lock out for fun.
 
No i couldnt really use the fga for anything as the boiler would only fire for 2 or 3 seconds at a time whilst fluctuating up and down.
 
No i couldnt really use the fga for anything as the boiler would only fire for 2 or 3 seconds at a time whilst fluctuating up and down.
Ensure condensate trap is clean on these, as will do the same fault also, did it make a hooting noise whilst firing?
 
Status
Not open for further replies.

Similar plumbing topics

There is 6 pipes under the boiler and one goes...
Replies
19
Views
1K
It worked! Brilliant and amazing! This has...
Replies
4
Views
1K
I feel for you, it's a bad position to be in...
Replies
18
Views
2K
You'd have to have gas meter removed if you...
Replies
19
Views
2K
Good job buddy. Rather than a beer, if you’re...
Replies
24
Views
3K
Back
Top