Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss working pressure at meter in the Gaining Plumbing Experience area at Plumbers Forums

I would say to contact the supplier and let them know as it should really be between 19mb and 30mb but they will probebly say everything is ok or maybe send someone out. Check you manometer is zerod tho first hahaha
 
30mb. Wow. Bet you cook your eggs in no time!
 
It may be a case of a faulty governor or just resetting but in Bexhill there are issues with working pressures as low as 17 mbar at the meter. This is down to inadequately sized pipes throughout the town and when you call Southern Gas Networks out there is nothing that they can do until the gas pipes have been renewed. You have to be really fussy with pipe sizing in Bexhill as you have hardly any leeway.
 
Working pressure at the meter between 19-30mbar? Think you will need to recheck those figures. :)
eh....i am asking you...i have 18mbar at the meter when the boiler is operating,the working pressures on the boiler are fine,is it ok to use or get esp in, 3 people liked it ,strange ,please explain
 
eh....i am asking you...i have 18mbar at the meter when the boiler is operating,the working pressures on the boiler are fine,is it ok to use or get esp in, 3 people liked it ,strange ,please explain


desrob, my statement re rechecking those figures for working pressure at the meter was in direct response to hobo's quote below. I apologise if I didn't make that clear.

I would say to contact the supplier and let them know as it should really be between 19mb and 30mb


The reason three people may have like my comment is because he was not describing correct tolerance for working pressure at the meter. In fact, he is describing tolerance for standing pressure. I didn't give the full correction immediately because I was hoping that he, or any one else learning from this threads, would check their reference material.

You have now identified correct working pressure tolerances. You have found that it is below the tolerance so I personally would have turned off the meter, issued the appropriate documentation, reported it to the Grid and got a job reference number. If the Grid chose to do nothing about it, I'm not the last (wo) man on the job.
 
Last edited by a moderator:
desrob, my statement re rechecking those figures for working pressure at the meter was in direct response to hobo's quote below. I apologise if I didn't make that clear.




The reason three people may have like my comment is because he was not describing correct tolerance for working pressure at the meter. In fact, he is describing tolerance for standing pressure. I didn't give the full correction immediately because I was hoping that he, or any one else learning from this threads, would check their reference material.

You have now identified correct working pressure tolerances. You have found that it is below the tolerance so I personally would have turned off the meter, issued the appropriate documentation, reported it to the Grid and got a job reference number. If the Grid chose to do nothing about it, I'm not the last (wo) man on the job.
you'll go green...apology
accepted
 
Don't know if this is relevant but Vaillant accept 16 MBar at boiler because they've found that there is some suction via fan through the gas valve. Having it at 16 makes it really helpful on pipe sizing the gas.
 
although it is correct that some boiler manufactures now state allowable figures below 20mb for inlet pressures at the inlet side of the gas valve, this does not excuse having more than 1mb drop from the meter and the appliance as required bu gas regs. Worcester for example will allow 16.5mb on some of its boilers. Taking into account 19mb at the meter, 18mb at the boiler isolator and a 1.5mb drop (16.5mb) across the gas pipework from its iso valve to test point on its gas valve.

This is the problem with manufactures stating low figures, some engineers will use this as an excuse to ignore undersized gas carcus. The best solution would be to include a test point at the isolation valve to ensure we can be sure we have got things correct.
 
18mbar.............at meter .....working pressure on boiler fine....is all ok....!

as other have said 18mb is too low and you normally need to call the grid. This said it can be allowable to have it lower than 19mb during peak periods. which if i remember correctly (but not 100% sure if correct) is a period of no longer than 5% of the total use of the appliance. I think there may be a technical buletin about this.

call the grid and let them decide if its ok.
 
Surely if mi says lower MBar at boiler its ok. I always thought mi,s over ruled every thing else. Surely this rule only applies to appliances that state it in mi,s. Fires cookers and not anything with a zero governor.
 
Most of the stated MI relate to losses inside the applaince before test point. MI does not overide the need for correct pipe sizing and never will. Especially when more than one applaince is installed in a property.
 

Similar plumbing topics

  • Question
A groundworker will normally do the whole...
Replies
3
Views
851
£64! I think I'll continue to use a pair of...
Replies
2
Views
184
Just do the same action again. Pot at Mac...
Replies
9
Views
1K
The Fluke 116 tests for micro amps, which is...
Replies
7
Views
658
Thank you for the replies. I had another...
Replies
4
Views
836
Back
Top