manx12
Installed a worcester bosch floor standing 550 in a 3bathroom house. During the commissioning process the standing pressure at meter was 24mb. when the boiler was put up to maximum temp/heating the working pressure at meter was 8mb.
The customer was made aware and transco was called out to check the meter/pipe etc.
when the transco guy comes he says to the householder "what is this semi industrial boiler doing in the house" (i was on another job when they arrived). And that the boiler need a huge amount of gas to work and that they need a new gas main putting in from the road.
Of course customer is back on the phone to me and i explained that it was a domestic boiler (basically it is a 42kw cdi with a hot water cylinder stuck on the side of it) and nowhere in the installation manual does it highlight a need for a new gas main..
Has anyone had an experiences of transco/national grid etc...
And any thoughts of solutions....