Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss zip pressure reducing valve operation in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
22
Thought I had a problem with an Ariston 30L water heater in a village hall whereby the hot water flow has steadily reduced to almost nothing over a period of a year. When you open the hot water tap you get a burst of water then it slows and stops after only a small amount has come out. Suspected blocked filter or outlet but all OK. Next suspect is what looks like a Zip pressure reducing valve (nominal 3Bar) with filter. Checked filter, clear and OK. Have not done a static pressure test yet on incoming cold but it may be less than 3 bar in the day. Does a 3 bar pressure reducing valve need more than 3 bar to flow or should it pass water and gradually shut off as the pressure increases to 3 bar. I can only get this one to flow by increasing the pressure setting well above the nominal 3 bar factory set point and that seems counter-intuitive.
 
No they don't need a min of 3 bar to operate they just won't reduce the pressure

Are you G3 registered?
 
If you put 2 bar through a P.Reg.V. set to 3 bar you'll get almost 2 bar through it. (minor internal losses)
 
Anything over 15 litre unvented needs G3 ticket, so hope you have it and a public building even more important
 
Anything over 15 litre unvented needs G3 ticket, so hope you have it and a public building even more important

Any water heater now mate
 
Blimey Shaun, I never knew that and I only renewed my ticket 10 mths ago. When did that happen?
 
Thought I had a problem with an Ariston 30L water heater in a village hall whereby the hot water flow has steadily reduced to almost nothing over a period of a year. When you open the hot water tap you get a burst of water then it slows and stops after only a small amount has come out. Suspected blocked filter or outlet but all OK. Next suspect is what looks like a Zip pressure reducing valve (nominal 3Bar) with filter. Checked filter, clear and OK. Have not done a static pressure test yet on incoming cold but it may be less than 3 bar in the day. Does a 3 bar pressure reducing valve need more than 3 bar to flow or should it pass water and gradually shut off as the pressure increases to 3 bar. I can only get this one to flow by increasing the pressure setting well above the nominal 3 bar factory set point and that seems counter-intuitive.
The pressure reducing valve is meant to maintain downstream pressure of 3 bar, irrespective of higher upstream pressure, within limits of design pressure, and maximum flow determined by size of valve. If the upstream pressure is below 3 bar it goes wide open, and flow falls off as the upstream pressure falls. Your symptoms look a bit peculiar.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
With the system as it is at the moment, I'd...
Replies
6
Views
2K
S
  • Question
Many thanks, Ben-gee - that's very useful...
Replies
2
Views
809
Steveo111
S
  • Question
No problem with reducing flow rates. The...
Replies
1
Views
925
  • Question
Apparently it worked fine before the TMV hot...
Replies
5
Views
3K
UPDATE Took the Comap valve out today. The...
Replies
17
Views
3K
Back
Top