i dont really get this use of the statement's "this manufacturer said this" and "this manufacturer said that".

it does not really matter what they suggest, a 15kw worcester or 15kw baxi or a 15kw whatever, no change in what is required. what matter's is you design/size the pipework correctly.

Most of what manufacturers state in there instructions is used by engineers as an excuse from my experience. If your using manufacturers instructions to help you decide or excuse what size gas supply you fit then you need to reevaluate your methods imo.
 
i dont really get this use of the statement's "this manufacturer said this" and "this manufacturer said that".

it does not really matter what they suggest, a 15kw worcester or 15kw baxi or a 15kw whatever, no change in what is required. what matter's is you design/size the pipework correctly.

Most of what manufacturers state in there instructions is used by engineers as an excuse from my experience. If your using manufacturers instructions to help you decide or excuse what size gas supply you fit then you need to reevaluate your methods imo.
i agree in part but it does matter what the manufactures say, worcester did say 22mm for a 12kw boiler and you had to comply ,now they say 15mm is ok,
You still need to size the house correctly.
 
i agree in part but it does matter what the manufactures say, worcester did say 22mm for a 12kw boiler and you had to comply ,now they say 15mm is ok,
You still need to size the house correctly.

the only thing the manufacturer has control over is the connection on the boiler. If you size the pipework correctly you will never not comply with the manufacturers instructions. All they are concerned about is low gas pressures when they attend a warranty call tbh which is why they sometimes state a min size to try and stop poor installs. You cant blame them for wanting to recommend a min pipesize when they attend alot of poorly fitted appliances.
 
Hi All,
Just trying to get some clarification on the 15 or 22mm gas connection. I have a colleague who insists on getting all his installs changed to 22mm. I have also had confirmation from clients that BG insist on this as well but I was working under the rule of pipe run with bends and other gas appliances at max being under 1mb drop from meter to boiler?
Most boilers appear to have 22mm connections but I am fitting a Glowworm flexicom this week that has 15mm gas connection, so do you always follow manufacturers instructions but hat applies when not mentioned in the MIs?
Thanks
Kewat66

size accordingly to inlet , op pressure but be prepared if any work is done on the property after you leave if the pressure drops below MI gas safe can make you go back upto 6 YEARS to change regardless of what any further work was done
 
I always change gas run to 22mm as long as the pressures required are met. I wouldn't leave 15mm in even if I was getting correct pressure at the boiler. Way I see it is, at some point in future it will be classed as undersized if it's left in 15mm so I might as well take the money for it than leave it for someone else.
Also in a similar vein if I change a lead tail on the meter I always increase to 28mm.
 
Status
Not open for further replies.

Similar plumbing topics

Thanks for the reply. I am going to get a...
Replies
14
Views
3K
Well if you are getting the gas meter moved to...
Replies
5
Views
3K
The boiler is just responding by limiting the...
Replies
8
Views
1K
Is it a bigger boiler than the old one ...
Replies
4
Views
3K
If you have the manufacturers instructions, go...
Replies
2
Views
2K
Back
Top