macka09

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,248
Hey guys. What’s the easiest way of determining that a 2 port motor has failed? I know that if the stat is calling and the arm is set to open on the valve and the actuator is ok it will fire. Is it purely a case of checking whether 240v is at the brown and orange when heat is called for? Any advice would be great. Electrics is a big weak point.
 
240 will be at brown if there‘s a demand, and then once opened 240 between blue and Orange. If the motor has failed, it won’t make the microswitch, or sometimes it can jump on the cogs.
 
Ok brilliant. I could always lock it open and use the stat to control it couldn’t I as temp measure. I’m just wondering if it’s locked open, when the other zone calls for heat will it also go onto the zone that’s locked open?
 
Bare in mind I don’t think all 2 ports contact the end switch when you lock it open. In that case you would need another functioning zone to bring on the boiler. The load will be shared then but if designed properly that’s not a problem.
The four or five Honeywell 2 ports that I've experienced don't close the contacts, possibly a safety feature as the manual opening/locking is to facilitate filling the system so don't want a empty boiler firing up if it hasn't been switched off.
 
I went and had a quick look earlier. It’s an Esi 2 port and the they’ve piped it in a way that you can’t get the head or cover off without removing the valve above. I was hoping it was going to be a stuck pin, but I couldn’t even quickly try to turn it with the head off. The three 2 ports go into a board on the cylinder and my electrics ent up to it. I’d change the whole valve if it was my own but I wanted to determine the signal from the stat to that valve.
 

Attachments

  • BFD7A5FC-4100-4978-A015-245A68F09D8F.jpeg
    BFD7A5FC-4100-4978-A015-245A68F09D8F.jpeg
    389 KB · Views: 39
If you can use a m.meter, ensure zone programmed on, remove the relevant stat cover, with stat turned down there should be 230V to one terminal (terminal to N or any E) with stat turned up should also be 230V from other terminal to N or E, or 0V between both terminals.
 
Try unplugging the rj45 style plug, see if there’s all the wires there, and then see if you can test directly on that pcb wiring center.
I’ll be honest the Pcb chugged me with the wiring. Everything else was working fine and the faulty valves was letting some residual heat pass. Which I assumed the valve was stuck. I was hoping to just turn up and free up the pin but no such luck lol
 
Two spanner’s and rotate the whole body
 
Two spanner’s and rotate the whole body
I didn’t have the time mate if I’m honest. I wasn’t going till Monday but thought it may be a 5 min job. Silly me. My thoughts were that the micro switch was the problem. Even in the closed position their was some residual heat going past the valve when the other zone was operating.
 
If it’s letting by, and not firing up the boiler, then it’ll be the valve, especially when you’ve said you couldn’t turn it by hand.
Sorry mate, I may be confusing everyone. I could operate the lever by hand, which returned to the closed position but even in the closed position and both zones calling for heat, only the top valve opened on demand. Some residual heat was getting past the faulty valve so I assumed the micro switch wasn’t making for the boiler to fire when only that zone was calling.
 
What does "top valve" refer to?. Are you saying that the faulty valve is opening on demand but the boiler isn't firing but if another zone is called for, the boiler fires up (as it should) and hot water will then flow through the faulty valve? (which it will, if its opened).
 
Sorry I thought I’d uploaded this pic for reference. The top 2 port is fine the one underneath is the faulty one. When the zone at the top calls for heat some residual manages to pass through the bottom of the 2 valves but the arm is in the closed position.
 

Attachments

  • 3908CD62-2796-47A6-9ED4-07BD76B1668B.jpeg
    3908CD62-2796-47A6-9ED4-07BD76B1668B.jpeg
    428 KB · Views: 32
You should feel a reasonable stiff resistance when pulling on the manual lever to open it and you may just hear the gears whirring when it re closes, but not much use if its not opening when energised.
 
What has happened with this site recently chaps. I’m on my phone but I just keep getting adverts pop up whilst scrolling the pages?
 
Typical. I can’t get a direct replacement off the shelf for these valves. I’ve not heard great things with ESI to be honest. Are there any other manufacturers that use the RJ45 connectors that may work do you know?
 
Oh ok. So cut the rj45 connector off from the valve and wire in the new valve to the cable going in to the Pcb. I get ya. Cheers chaps. The Regin connectors look bloody fiddly lol
 

Similar plumbing topics

https://www.NoLinkingToThis/p/drayton-27101sx-3-po...
Replies
1
Views
2K
Most likely the 3-port, but make sure there's...
Replies
2
Views
1K
    • Like
From this post, I think you’ve got a good...
2
Replies
47
Views
6K
D
I would personally also get heating engineer...
Replies
2
Views
3K
Aquarius
A
Back
Top