Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss 3 port valve trouble? in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
19
Hi all, first post so please bare with me!
Working at a house on saturday, removed 3 rads, filled and bled system (open vent system,pumped with a y plan 3port valve ) turned hotwater on, worked fine, but couldnt get the boiler to fire or the pump when i called for central heating?
Tested the 3 port, (siemens) with the programmer on c/h only the room stat to max, the orange wire was dead, the white wire live, can anyone confirm my suspect of a faulty 3 port that needs replacing?
Thanks in advance
Andrew
 
not always a motor. a motor can still be winding across and making contact with micro switch, but micro swtch faulty or the board.

you'll need to check for power at the motor and see is motor is working on heating call.
 
should be a lever on the bottom of the valve.
switch the heating on pull the lever to manually turn on the heating. if the heating comes on surely this means the motors faulty
 
as you say move the lever to man and boiler should kick in if not then yes i would look at the motor.
trouble is op has not given enough info for an exact fault to be given.
could also be seized spindle in hw only.
 
If you say the orange wire is dead ,that is the wire which operates with the pump and boiler. it shouldnt be dead, sounds like you have an electrical fault.. Did you say when the stat is turned on full it still dosent fire up the boiler?

You can get a second opinion, but every veiw counts..:)
 
Thanks for the replys, it seems that it may be stuck in hot water port, as the lever when moved dosent engage with anything,the stat was up to full and controller on c/h only but nothing happened.I think this must be the valve and moter at fault, failing that the signal from the controller?!
 
it won't be stuck in hot water port if your getting hot water more likely to be in mid position.
if the lever has no resistance on it its in mid position.
if you have live on the white its not the controller.

sounds like its seized in mid position but not making contact with the microswitch.

change the brass valve or a complete unit.
 
Some misinformation here I think. These three port valve in their 'rest' position allow a path to the HWC but not the central heating. If it were stuck in mid-position then there would be heating as well. Sometimes the valve sticks and stops the motor. If the motor is demountable then I would suggest you demount it and then try. If the boiler fires in heating only mode then the valve is sticking, though it may well have damaged the motor. If the boiler doesn't fire then check the valve part manually for free movement and if OK just replace the motor.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Its a very ingenious but devilishly cunning...
2
Replies
25
Views
3K
https://www.NoLinkingToThis/p/drayton-27101sx-3-po...
Replies
1
Views
2K
Air locked air is a pain sometimes just need...
Replies
10
Views
2K
  • Question
3 port could be on its way out?
Replies
3
Views
2K
Deleted member 120897
D
200% won’t be the reason the cylinder isn’t...
Replies
10
Views
1K
Back
Top