Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Advice really appreciated on hot water temperature in the Bathroom Advice area at Plumbers Forums

Messages
10
Hello people in the know! I have just moved into a new house. It is a system I am not used to as my previous home had a combi boiler. So, there is a large blue hot water cylinder in the airing cupboard and the dial on the front is set to 65. There is a Valiant Ecotec 418 Boiler in the kitchen and the water dial is set to 65 (it doesn't go higher than this).
I have the water set on a timer to come on at 5pm for one hour.
It just doesn't seem hot enough. So . . . can I turn up the temperature on the front of the blue hot water cylinder or is it governed by the 65 setting on the boiler. Also, how long should the water stay hot for? The system was installed by the previous owner in 2014.
Many thanks for any advice you can give. All the best Jan
 
Hi Chris - thank you for your reply. Its a big one! (see pic) My neighbour has had a look and says the pipe to the tank from the 3 port valve(?) is hot so thinks my boiler is faulty - but he's not a gas engineer so I wanted to get some advice before calling out an engineer

20190122_200739.jpg
 
LOL @ Brexit stockpile! Hand hot but not hot enough that I need to pull my hand away.
My sister has a similar system but only has her water on for half an hour and its roasting! Ho hum.
Thanks snowhead . . . will try to put it on for longer :)
 
Hi Chris - thank you for your reply. Its a big one! (see pic) My neighbour has had a look and says the pipe to the tank from the 3 port valve(?) is hot so thinks my boiler is faulty - but he's not a gas engineer so I wanted to get some advice before calling out an engineer
Hi Jean :D you don't have a 3 port valve, you have zone valves. When the timer is calling for hot water then the pipe should be hot to the cylinder, if your hot water isn't on but your heating is then it could also be convection heating the pipe up. If your unsure or concerned then best to call an engineer in to check the system over.
 
if the boiler only supplies water at 65c the cylinder would take a while longer to get up to temperature, traditional boilers would go up to 80+. If that's as high as it goes you'll have to give it plenty of time.
However having said that all the pipes around the valve should be red hot when it's running so it could be either a circulation or a valve issue.
 
Not trying to get you to spend money however when was it last serviced? Maybe a service and a full explanation of what`s what would help you.
 
Last edited:
The water being 'hot enough' is subjective. You could measure the temperature at the hot tap - it will probably be roughly 10 degrees lower than the cylinder is set to, because of heat loss before it gets there.

If your boiler is only set to 65 degrees, though, it'll short cycle before the cylinder has fully heated up. The boiler flow temperature should be roughly 10 degrees higher than the cylinder stat temperature to allow adequate heat transfer.
 
if the boiler only supplies water at 65c the cylinder would take a while longer to get up to temperature, traditional boilers would go up to 80+. If that's as high as it goes you'll have to give it plenty of time.
However having said that all the pipes around the valve should be red hot when it's running so it could be either a circulation or a valve issue.

It's the cylinder stat that's set to 65 not the boiler ;)
 
The hot water (tap) dial on your boiler has no effect, it is not used in this country on the regular or system boilers only the comb's.
You will need to have the heating (rad) one turned up to at least 70 so it can heat the domestic hot water up to the required 60 -65 deg C.
 
The hot water (tap) dial on your boiler has no effect, it is not used in this country on the regular or system boilers only the comb's.

Unless paired with a VR65/VR66 and VR10 sensor, in which case the HW dial directly controls the set temperature of the cylinder. And the flow rate is automatically boosted to 80 degrees when heating the cylinder.

I agree, though, that unless the Vaillant controls and sensor have been adapted to work with a non-Vaillant Unistor cylinder, the radiator dial on the front of the boiler will control flow temp to the cylinder and must be set approx 10 degrees higher than the cylinder stat.
 
Last edited:
Going back to what @johnduffell mentioned.
The target temperature of the cylinder is the same as the max temp of the boiler. Therefore the cylinder will struggle to get there due to the fact that there are heat losses. The coil / heat exchanger in the cylinder needs to be hotter than the water temperature you're aiming at otherwise it will never reach it, or it may do over time.

The Vaillant boiler maximum temperature on the stat can be altered. They come factory set to 75 but will go up to 80 or down to 40.
You may want to get a Gas Safe Engineer to service it and check it over and then raise it back to 75. You could raise it yourself I have no doubt but there may be a reason the previous owner set it so low?

Hope this helps.
 
Hello - thank you for all your replies. The boiler was last serviced in October 2018. The water temp on BOILER is set to 65 and the rads temp on BOILER is set to 57. The thermostat on the front of the HWcylinder is set to 65. I've upped the timer to 1.5 hours.
 
and the rads temp on BOILER is set to 57. The thermostat on the front of the HWcylinder is set to 65. I've upped the timer to 1.5 hours.

With the boiler set to 57, the Cylinder stat will *never* be satisfied. You need to set the boiler to 75.

This is one of the compromises of having a cylinder which requires a high flow temp and a CH system which can run on much lower flow temps. The only way around this is to use the Vaillant controls or OpenTherm controls (though your boiler would require a separate OpenTherm module for this).
 
Hello - thank you for all your replies. The boiler was last serviced in October 2018. The water temp on BOILER is set to 65 and the rads temp on BOILER is set to 57. The thermostat on the front of the HWcylinder is set to 65. I've upped the timer to 1.5 hours.

The Water temp dial on the Vaillant will not work unless you are using the correct Vaillant controls. I must have skim read the post as I did not see 57 deg mentioned earlier. As @fezster says, if boiler flow temp is below the target cylinder temp, it cannot get the cylinder up to the required temp.
I was talking about the settings on the dial itself. I had taken it that you meant the dial will not turn up past 65 degrees. On the Vaillant boiler you can alter the maximum setting the dial will go to. Meaning that if you turn the dial fully clockwise until it stops, the max temp you can set it too was 75 from the factory but that setting can be altered from 40-80 degrees.
Can you turn the CH dial to 75?
If so try setting it on that for a day or so to see if it does the job. If it does, ask an Engineer to look at the set up of the system. You don't really want higher temperatures with a condensing boiler if you can help it. They will be less efficient on the Heating side.
 
I was talking about the settings on the dial itself. I had taken it that you meant the dial will not turn up past 65 degrees. On the Vaillant boiler you can alter the maximum setting the dial will go to. Meaning that if you turn the dial fully clockwise until it stops, the max temp you can set it too was 75 from the factory but that setting can be altered from 40-80 degrees.
Can you turn the CH dial to 75?

I believe OP has said it's the HW dial they are trying to adjust.

As you say, the CH dial can be adjusted to 75 from the factory and also modified through the installer menu to allow higher.

The HW dial will be restricted to 65 as it is used to control the cylinder temperature (if used with Vaillant controls). I can't remember just now (and I'm not in front of my boiler) but I think the HW dial is only restricted to 65 if and when a VR10 is attached.

OP - can you please confirm (or take pictures) of the various controls you have, as this will determine whether it's the HW dial or the Radiator dial you need to be adjusting on your boiler.
 
OK - pic attached - the HOT WATER DIAL ON THE BOILER only goes up to 65 and that is what is it set to. The CH DIAL ON THE BOILER is set to 57. Shall I increase the CH DIAL ON THE BOILER AS THIS DOES GO UP TO 75 - thank you. Jan :)


I believe OP has said it's the HW dial they are trying to adjust.

As you say, the CH dial can be adjusted to 75 from the factory and also modified through the installer menu to allow higher.

The HW dial will be restricted to 65 as it is used to control the cylinder temperature (if used with Vaillant controls). I can't remember just now (and I'm not in front of my boiler) but I think the HW dial is only restricted to 65 if and when a VR10 is attached.

OP - can you please confirm (or take pictures) of the various controls you have, as this will determine whether it's the HW dial or the Radiator dial you need to be adjusting on your boiler.

20190122_200719.jpg
 

Similar plumbing topics

  • Question
That’s good, we’ll persevered! Let us know...
Replies
11
Views
1K
B
No the installers need to come out
Replies
10
Views
2K
L
That shouldn't happen. Going to need lots of...
Replies
1
Views
227
Replies
8
Views
770
Yes it will be controlled on boiler thermostat.
Replies
3
Views
566
Back
Top