Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Air in towel radiator in the Air Sourced Heat Pumps area at Plumbers Forums

Messages
25
Our upstairs towel radiator keeps filling with air at the top. We had a new system boiler, new tank and new pipework fitted in October. The new tank is in the garage which is underneath the house and the new boiler is in the kitchen at ground floor level. We also had underfloor heating installed in our kitchen, the manifold is in the garage under the house. The 3 towel radiators come on when either the hot water is on or the underfloor heating is on, but not when the other radiators are on. We keep needing to let air out of the upstairs towel radiator and top the boiler up with water at the same time. The pipes in the walls and under the floors are no longer easily accessible. Where is the air coming from and how do we fix it? Please help!
 
It’s something they should of been aware of. All system/combi boilers only come with a reasonably small vessel. Quite often the system volume is too much for a standard fitted vessel. A few factors help arrive at a suitable size. System volume, operating temperatures, min and max running pressure. The maths enables you to arrive at an accurate answer for that current system but there is no such thing as too large a vessel, the only problem is additional cost for larger than needed vessels and siting them.
As for the air problem. You did reply to my previous comment about plastic pipe. I would like to think it’s barrier pipe that’s been used?
 
It’s something they should of been aware of. All system/combi boilers only come with a reasonably small vessel. Quite often the system volume is too much for a standard fitted vessel. A few factors help arrive at a suitable size. System volume, operating temperatures, min and max running pressure. The maths enables you to arrive at an accurate answer for that current system but there is no such thing as too large a vessel, the only problem is additional cost for larger than needed vessels and siting them.
As for the air problem. You did reply to my previous comment about plastic pipe. I would like to think it’s barrier pipe that’s been used?
 
Ok thanks, could the lack of a second vessel be causing the air intake? I have a photo of the plastic pipes..the horizontal sections lead to a towel rail on the other side of the wall, the rest of the pipework outside of this photo is copper.
 

Attachments

  • 442F3747-C9AD-474A-A65F-CE90566266D6.jpeg
    442F3747-C9AD-474A-A65F-CE90566266D6.jpeg
    417.6 KB · Views: 53
Ok thanks, could the lack of a second vessel be causing the air intake? I have a photo of the plastic pipes..the horizontal sections lead to a towel rail on the other side of the wall, the rest of the pipework outside of this photo is copper.
Better quality photo…
 

Attachments

  • 321F3519-E656-4759-A8AC-121C7F8A4198.jpeg
    321F3519-E656-4759-A8AC-121C7F8A4198.jpeg
    627.3 KB · Views: 49
No the lack of an additional vessel is not going to be the cause of air ingress. A poorly positioned pump in relation to vessel location can cause frequent venting of radiators but that’s a pressure problem and not air ingress.
I honestly can’t identify that plastic pipe.
 
No the lack of an additional vessel is not going to be the cause of air ingress. A poorly positioned pump in relation to vessel location can cause frequent venting of radiators but that’s a pressure problem and not air ingress.
I honestly can’t identify that plastic pipe.
Ok thanks. I’m assuming the pump is in our garage with the tank?….the boiler is up one floor & approx 9m away horizontally.
 
Overall your installation seems ok it's easy to criticize and we all have our working practices , I personally don't think the use of plastic pipe is a cause of air ingress it looks like speed fit pipe and fittings that have been used which are reliable and have been used widely for years , any pipework around the cylinder hot or cold should be insulated as should any pipework in cold areas and voids , your heating pump will be inside your boiler casing the property seems like a large family home and a system boiler with a internal pump wouldn't of been my choice as these boilers struggle to move the volume of water in the system and absorb the expansion there are ways to improve this and I can see why maybe it was fitted because there is not much space , has the system always been problematic ? is the work completed ? we could advise ways to improve your system but it's really the installers responsibility to make sure its commissioned and working correctly you plan to extend your home further and this without doubt will cause more problems unless improvements are made . Regards kop 👍
 
Last edited:
Overall your installation seems ok it's easy to criticize and we all have our working practices , I personally don't think the use of plastic pipe is a cause of air ingress it looks like speed fit pipe and fittings that have been used which are reliable and have been used widely for years , any pipework around the cylinder hot or cold should be insulated as should any pipework in cold areas and voids , your heating pump will be inside your boiler casing the property seems like a large family home and a system boiler with a internal pump wouldn't of been my choice as these boilers struggle to move the volume of water in the system and absorb the expansion there are ways to improve this and I can see why maybe it was fitted because there is not much space , has the system always been problematic ? is the work completed ? we could advise ways to improve your system but it's really the installers responsibility to make sure its commissioned and working correctly you plan to extend your home further and this without doubt will cause more problems unless improvements are made . Regards kop 👍
 
Thanks kop. Which boiler should we have had? Prior to this we had a standard boiler & hot water tank (not pressurised system) & had no problems. We went for system as we were told it was better for 2+ bathrooms (we have 2 bathrooms at the moment). We were told our old boiler probably couldn’t handle the underfloor heating. So if we get another expansion vessel fitted is this enough? We can lag the visible pipework ourselves, under the floors is a bit tricky now. Is there anything else that needs changing? Is the likely cause of the air ingress a leak or is there anything else we could do to try to stop the air getting in?
 
Thanks kop. Which boiler should we have had? Prior to this we had a standard boiler & hot water tank (not pressurised system) & had no problems. We went for system as we were told it was better for 2+ bathrooms (we have 2 bathrooms at the moment). We were told our old boiler probably couldn’t handle the underfloor heating. So if we get another expansion vessel fitted is this enough? We can lag the visible pipework ourselves, under the floors is a bit tricky now. Is there anything else that needs changing? Is the likely cause of the air ingress a leak or is there anything else we could do to try to stop the air getting in?
Yes, the work is completed & there’s space in the garage for another expansion vessel. The water tank was originally upstairs in the airing cupboard, now moved to the internal garage to allow stairs to be built to the loft. The boiler before & now is in a kitchen cupboard (no top & bottom to the cupboard).
 
What you have been told is correct a sealed system boiler and unvented cylinder is the best choice for your property you're boiler is not necessarily wrong it's not unusual to use a system boiler but it needs piping a different way , you will need a extra expansion vessel to accommodate the volume of heated water in the system, the insulation needs doing just do what is visible and easy to access I would get this completed first fit the aav's, future improvements can be made if necessary.
 
There seems to be 2 x red exp. vessels and 1 x white, one red is adjacent to the boiler?, what volume is this.
You can tell easily if the installed exp. volume is sufficient by turning on all heating systems and noting the boiler pressure when all systems hot, if not > 2.5bar then OK from a expansion point of view but maybe other reasons for installing extra one?.
Can you also post a close up photo of the UPM pump, when its running, don't know if its running on one of its manual modes or is PWM controlled.
 
Last edited:
What you have been told is correct a sealed system boiler and unvented cylinder is the best choice for your property you're boiler is not necessarily wrong it's not unusual to use a system boiler but it needs piping a different way , you will need a extra expansion vessel to accommodate the volume of heated water in the system, the insulation needs doing just do what is visible and easy to access I would get this completed first fit the aav's, future improvements can be made if necessary.
Thank you. What other improvements would you recommend? And how to we fix this annoying air ingress?
 
There seems to be 2 x red exp. vessels and 1 x white, one red is adjacent to the boiler?, what volume is this.
You can tell easily if the installed exp. volume is sufficient by turning on all heating systems and noting the boiler pressure when all systems hot, if not > 2.5bar then OK from a expansion point of view but maybe other reasons for installing extra one?.
Can you also post a close up photo of the UPM pump, don't know if its running on one of its manual modes or is PWM controlled.
???
 
There seems to be 2 x red exp. vessels and 1 x white, one red is adjacent to the boiler?, what volume is this.
You can tell easily if the installed exp. volume is sufficient by turning on all heating systems and noting the boiler pressure when all systems hot, if not > 2.5bar then OK from a expansion point of view but maybe other reasons for installing extra one?.
Can you also post a close up photo of the UPM pump, when its running, don't know if its running on one of its manual modes or is PWM controlled.
The photos of the red ones are not my house. Pressure does not go over 2.5. What is the UPM pump? The black box near the water tank?
 
The photos of the red ones are not my house. Pressure does not go over 2.5. What is the UPM pump? The black box near the water tank?

Apoligies, the red ones are atypical as shown by KOP.

2.5bar is OK for the moment as long as you don't install any more rads etc.
Re Air venting, when you vent the air, then theoretically, if you don't top up the system, if air is entering the system the pressure should build up again, if it doesn't then perhaps air still in the UFH loops even though this might be unlikely since last October, anyway, after the next venting do not top up except that the pressure is excessively low and see what happens.

The Pump is on the UFH manifold as shown, you might post a close up photo of it when running to show the LEDs.
Also if you can see the UFH manifold, the flow rates for each loop and the manifold flow and return temperatures, if available.
 

Attachments

  • Pump UPM3.jpeg
    Pump UPM3.jpeg
    705 KB · Views: 42
Thank you 👍
One other thing to try is tie wrap a plastic bag on the end of the safety valve of the boiler for 24 hrs run the system heat the water and just monitor if any water is in the bag ? I am working on a large 5 bed house on a insurance job this is a more typical install I have to add I didn't install it but I know the Engineer who did 👍
 

Attachments

  • IMG_20220224_103050094.jpg
    IMG_20220224_103050094.jpg
    411 KB · Views: 44
"We also had underfloor heating installed in our kitchen, the manifold is in the garage under the house. "

I thought it was necessary for a UFH manifold to be installed ABOVE the UFH pipes that it supplied? Usually, the manifold has an auto air vent, but if this is below the underfloor heating, it wouldn't have any effect as air rises to the highest point, possibly to the top of the towel rails.

I assume the affected towel rails are at the highest point in the heating system?

What would happen to an auto air vent on an UFH manifold that was installed lower than the UFH? Is it possible air could get into the system? I suspect not, but this is the only thing that jumped out at me regarding your setup.
 
Aslong as it’s purged of all air the ufh will work fine if the pipe is above the manifold
 
Thanks all, after letting the air out of the towel rails several more times the problem seems to have resolved. I think it may have been air trapped in the system from the installation but will keep an eye on it.
There have been numerous posts about air collecting in towel rails, is it because the top(s) of the towel rails are generally higher than any other rad top(s)?.
 

Similar plumbing topics

S
  • Question
Air keeps collecting in our upstairs bathroom...
Replies
0
Views
1K
Sammy1
S
  • Question
Red circles show my new AAVs and the manual...