Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Air testing soil stack in the Boilers area at Plumbers Forums

Status
Not open for further replies.
Messages
25
Hi all,

I'm thinking of renewing the old cast iron soil stack on our house when carrying out renovations in our bathroom (which involves moving the positions of the sanitaryware so it's quite extensive).

I read that all new soil stack installations should be air tested using a 'U' gauge in accordance with Part H of the Building Regulations.

I was wondering what folks on this forum thought of this? Is it commonly carried out?

Is it performed once everything is plumbed in, because if this is the case and a fault was found there could potentially be quite a lot of hassle tracking down where it lies, especially if it's under the floor.

Thanks in advance for any replies/advice.

Tony.
 
No, once you've got it up and the oulets into the bathroom, bung up the ends and do the test. You can get the test gear from most hire shops.
 
yes if renewing soil stack it does need to be done to check for air leaks it needs to be done after everything is is put in because you need to have your seals in place (ie sink basin toilet) to create pressure of 38mm for 3 minutes
 
yes if renewing soil stack it does need to be done to check for air leaks it needs to be done after everything is is put in because you need to have your seals in place (ie sink basin toilet) to create pressure of 38mm for 3 minutes

Thanks for the info.
How would you go about carrying out the test once everything is plumbed in? Where would the test gear fit into the system?

Again, thanks in advance for the help.

Tony.
 
Hi. Plug off the vent and base of stack (via rodding eye) Using a U tube. Pass the hose of the U tube through the water trap in the wc. so as the end is in air within the soil system. Do the same with plain hose and blow down it until you have 1.5" Wg on U tube (manometer) if there is no drop in pressure thats it done. Good Luck
 
Hi. Plug off the vent and base of stack (via rodding eye) Using a U tube. Pass the hose of the U tube through the water trap in the wc. so as the end is in air within the soil system. Do the same with plain hose and blow down it until you have 1.5" Wg on U tube (manometer) if there is no drop in pressure that's it done. Good Luck

Thanks very much for that descriptive explanation.
I'll print it off and use it when the time's right.

Thanks again,
Tony.
 
Status
Not open for further replies.

Similar plumbing topics

Should have it done in a day. If you’re a bit...
Replies
5
Views
17K
G
  • Locked
Larger diameter pipes. Old cast often had only...
Replies
1
Views
10K
kay-jay
K
M
  • Locked
Sounds like no cleaner then inhibitor to me.
2
Replies
45
Views
6K
Back
Top