I've had a cupl of customers order the pcb's online for various faults .. one being a pump overrun issue. It saves waiting in for the delvvery and any potential warranty problems being pointed your way..... And NO, custard orders and you fit 🙂
Regards the fault. If I suspected the overrun I'd want to be checking the system from cold! Put into water only and fire up. Hands on flow and return to check how well the system was circulating. If no serious temp diff then I'd continue to run on hot water only to get the boiler up to max temp ASAP. If overrun issue is what you're testing for then you need to be either checking the pump or have your multimeter on the pump live&Neutral at the terminal strip on the boiler. there needs to be a constant 230v. If the noise starts in conjunction with the power dropping out then you know the overrun relay on the pcb is gooshed!!! Thing is with intermittent faults it's not guaranteed to happen all the time!!!
Check it from cold mutley racers ... f&r temp diff on h/w only will tell you how well the boiler is circulating from start-up till fail...!
Awesome. Thanks. Will give this a go. Exciting