Hope someone can suggest where I should looking to resolve this one...
I have a Bosch 30Cdi regular boiler on an S plan system with a 180L vented, indirect hot water cylinder.
Boiler Temperature is set to 5 (67c) and the stat on the Hot water cylinder is set just below 60c.
A Honeywell DU144 Auto Bypass valve is fitted and set to 0.55 to give a minimum flow of 300l/hr through the boiler at Speed setting 3 on a Grundfos UPS2 15-50/60 circulator.
From cold, when the stat on the cylinder calls for heat, the motorised valve opens and starts the boiler.
The flow temperature on the boiler rises to around 60c within a few minutes, finally getting to 69c before modulating down to 67c.
Within 10 minutes, I measured temperature at the 22mm pipe into the cylinder coil, which was 64c and the pipe out of the coil was 60c.
These temperatures were also reflected at the boiler on the 28mm Flow and Return pipes.
As time went on, the temperature flow out of the coil and return to the boiler got ever closer to the flow temperature. Flow temperature from the boiler was measured at 64c and the Return temperature was measured at 62c.
After half an hour the boiler switched off (while still displaying a Flow temperature of 67c).
The cylinder stat had not been satisfied, the motorised valve was still open and the circulator continued to run.
After a period of time and the Boiler Flow temperature had reduced to approx. 55c, the boiler started up again and continued to heat the cylinder until, once again, the boiler short-cycled.
After a few short-cycling events, the cylinder stat was eventually satisfied, the motorised valve closed, the boiler switched off and the circulator ran on for a period.
Looking back through my Smart Meter records, this has been happening for some time and ends up using around 11KWh of gas, which isn't very efficient or cost effective!
Am I not displacing enough heat through the coil in the cylinder, is the pump running too fast, is temperature setting on the cylinder stat too close to that of the boiler temperature or should I be looking elsewhere?
Any advice appreciated.
I have a Bosch 30Cdi regular boiler on an S plan system with a 180L vented, indirect hot water cylinder.
Boiler Temperature is set to 5 (67c) and the stat on the Hot water cylinder is set just below 60c.
A Honeywell DU144 Auto Bypass valve is fitted and set to 0.55 to give a minimum flow of 300l/hr through the boiler at Speed setting 3 on a Grundfos UPS2 15-50/60 circulator.
From cold, when the stat on the cylinder calls for heat, the motorised valve opens and starts the boiler.
The flow temperature on the boiler rises to around 60c within a few minutes, finally getting to 69c before modulating down to 67c.
Within 10 minutes, I measured temperature at the 22mm pipe into the cylinder coil, which was 64c and the pipe out of the coil was 60c.
These temperatures were also reflected at the boiler on the 28mm Flow and Return pipes.
As time went on, the temperature flow out of the coil and return to the boiler got ever closer to the flow temperature. Flow temperature from the boiler was measured at 64c and the Return temperature was measured at 62c.
After half an hour the boiler switched off (while still displaying a Flow temperature of 67c).
The cylinder stat had not been satisfied, the motorised valve was still open and the circulator continued to run.
After a period of time and the Boiler Flow temperature had reduced to approx. 55c, the boiler started up again and continued to heat the cylinder until, once again, the boiler short-cycled.
After a few short-cycling events, the cylinder stat was eventually satisfied, the motorised valve closed, the boiler switched off and the circulator ran on for a period.
Looking back through my Smart Meter records, this has been happening for some time and ends up using around 11KWh of gas, which isn't very efficient or cost effective!
Am I not displacing enough heat through the coil in the cylinder, is the pump running too fast, is temperature setting on the cylinder stat too close to that of the boiler temperature or should I be looking elsewhere?
Any advice appreciated.