Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiler keeps short cycling with only UFH is on in the Boilers area at Plumbers Forums

Eg

1695398137614.png
 
One of the CCT (or LLH) advantages is that the primary circulating flow can be controlled to give a flow high enough to control the maximum dT which can exceed the boilers max allowable, generally ~ 25C, another advantage is that it helps to get the boiler away without exceeding the flow temp tripping point since all gas boilers fire up at ~ 65% of max output for up to 60 secs before modulation. The disadvantage is that the boiler return temperature increases with reduced demand.
For example if you set the primary flow to 14.3LPM to give a dT of 20C with a 20KW rad demand, the boiler dT will be 20C with flow/return temps of 65C/45C, a rad demand of 9kw will result in a dT of 9C, flow/returns of 65C/56C, a UFH demand of 9KW will result in the same dT of 9C with flow/return of 65C/56C. A rad demand of 2.5KW will give a dT of only (theoretically0 2.5C with flow/return of 65C/62.5C and the same for a UFH demand of 2.5KW.
Of course it will not prevent cycling if the minimum boiler output is greater than the heating demand.
 
Is a CCT/LLH required?.
The above boiler, a Vaillant 438, has a HEX with dP of 4.05M at a flow of 27.2LPM.
If a manual bypass was installed then opening it to give a 10.7LPM permanent by pass will result in a HEX dP of 3.5M (at 25LPM) which leaves 4.5M (8M UPS2 installed) remaining head to circulate 14.3LPM through the rads etc.
You will then end up with (boiler) flow/returns of rads only 65C/53.5C, dT 11.5C, UFH 9kw only of 65C/60C dT 5C, UFH 2.5KW 65C/63.5C, dT 2.5C..

If you could source a true constant curve pump then a ABV could be used to get much improved, lower boiler return temperature and greater boiler efficiency.
 
Last edited:
@ShaunCorbs - thanks for this.

From the diagram you provided, would:
  1. the 'heat source' be the equivalent of the new system boiler and the 'primary circulator be the internal pump within the system boiler?
  2. where it shows the "secondary circulator along with the 'spring loaded check valve' - would this be for the CH or UFH?
  3. and for the "another secondary circuit" - would this be for the UFH or CH?
  4. from the two secondary circulator pumps shown on your diagram, where would I use my existing 25-80 pump?
  5. similarly, where you mention about the need for an additional 15-5/60 pump for the UFH, where would this be located?
If you were able to provide a quick sketch of how my system should be set up, this will be greatly appreciated.

At the end of the day, what I am trying to achieve is to be able to run the UFH on its own without the boiler continually cycling. When this happens, the room that contains the UFH hardly heats up so the way I get around this is to run the CH at the same time so that the boiler continually runs and the UFH room heats up.

I had a look at the latest Vaillent ecotec plus system 25kW boilers which have a modulation range of 1:10 ecoTEC Plus - https://www.vaillant.co.uk/for-installers/products/ecotec-plus-610-615-620-625-630-635-154880.html. I was wondering if this would reduce the boiler cycling with just the UFH on?
 
That would be the rads as it’s the hottest heat load

Then the ufh eg horizontal one

25-80 for the rads

15-60 for the ufh

Same as drawing horizontal set

You want the highest modulation possible eg lowest kw figure of ideally under 1kw if possible

Only just seen you sent me a only sorry will have a look later
 
sorry @ShaunCorbs but I don't fully understand your reply based on the diagram you provided.

From your diagram:
  • where it shows the "secondary circuit & circulator along with the 'spring loaded check valve' - is this the CH circuit and the secondary circulator being my existing 25-80 pump?
  • where it shows the "another secondary circuit" - is this the UFH circuit, and where the pump is shown, is this the additional 15-5/60 pump you refer to, for the UFH?
 
Will draw it out tonight for you
 
can do it two ways eg below
 

Attachments

  • Hydronic CCT.png
    Hydronic CCT.png
    41.8 KB · Views: 44
  • System CCT.png
    System CCT.png
    13.8 KB · Views: 40
many thanks @ShaunCorbs. On the Hydronic CCT, stupid question but what do the symbols (attached) denote? From your diagram last week, you showed the position of two CCTs, spring-loaded check valve and purging valve - where would these appear on the Hydronic CCT diagram?

On the System CCT diagram, I just see the 25-80 pump but do not see the 15-80 pump, nor the CCTs, check & purging valves - I they not needed?

Are there any advantages with the Hydronic CCT setup over the System CCT setup, and vice-versa?

1695885589029.png
 
Check valve / swing check

As the boiler is cct you only need one pump ideally a modulating pump is best and no there not m

Both the same
 
You will need a check valve to stop reverse circulating as you don’t have a zone valve you could fit a zone valve but a check valve / swing check is cheaper

The purge valves etc arnt needed don’t know why there’s a m on the end tho
 

Similar plumbing topics

@ShaunCorbs - the heating engineer who will be...
Replies
6
Views
913
well, I really cannot see what extra features...
Replies
10
Views
1K
Finally (I hope) got to the bottom of this...
2 3
Replies
55
Views
5K
Anyway, you can always increase the boiler...
Replies
16
Views
1K
Set the ufh mixer to 30-40 / what the design...
Replies
1
Views
2K