Thanks for this. I was thinking in my novice mind that this pump flow issue could be an issue too.First rule of LLW design. “Thou shall not use multi tapping headers” Sorry but they are a PIN. And if systems arent perfectly matched and flow rates set correctly will leave you wide open to parasitic flow across the ports.
First thing I’d be checking is flow rate of your primary pump, Vs flow rate of your secondaries.
Something is pulling that flow water across the header rather than it circulating around it, so boiler then is ramping up as it’s running on its thermistor readings to control the gas rate. If the heat is going around the system rather than round the header it’s going to take an awfully long time before the temps are coming back to the boiler hot enough to start the modulation process
Guide to low loss headers - CIBSE Journal
Achieving hydraulic separation through well-designed low loss headers is key for efficient heating and cooling systems. David Palmer and Baxi Heating’s Ryan Kirkwood provide detailed design guidance, including a recommended system configurationwww.cibsejournal.com
The heating pumps are Grundfos Alpha 2s. The boiler pump is currently set to max constant pressure -
The UFH has been set to speed 1 of 3
CH to low constant pressure (I tried proportionate pressure but then it takes too long to heat the rads)
Towel rails to low constant pressure
HW to max constant pressure
I'm not sure how to check the flow rates of the pumps or circuits.
For example this weekend I noticed that for a couple of hours when just the CH circuit was calling for heat, the boiler was getting too hot and cycling. The same thing happens if only the UFH is calling for heat.
I have been trying to time the heating circuits to call for heat at the same time, which in combination with the low range rating (40% of 40kw) means the boiler only achieves a flow temperature of around 50 rather than 65/70. This lower flow temp isn't conceptually a bad thing I think (?) because the UFH mixes down to a lower flow temp anyway, and the rads can manage with 50 degrees too.
The problem is if the CH or Towel Rails also kick in, then there can be too much demand of on 16kw heat output currently from the boiler. Then the HW stays on for a really long time because it cannot heat the tanks to 50 degrees with a 50 degree flow temp.